Confused - 2nd Zone Heats up but no pressure reading on external pressure gauge
#1
Member
Thread Starter
Join Date: Oct 2013
Posts: 43
Received 0 Votes
on
0 Posts
No water in 2nd zone pipes (2nd Floor)
Burnham hydronic boiler:
Was purging system of air after I replaced the pump.
Here are some pictures



1. I manually opened 1 zone valve and closed the 2nd zone. Purged the system and refilled the 1st system. Used an external pressure guage to check the pressure through the hose faucet. Pressurized the system to 15 psi.
2. Shutoff the 1st zone and opened the 2nd zone. No water drains from the system. Adding water just increases the pressure reading from the boiler. I didn't go above 20 because I feared the pressure relief valve would open. (I'm assuming most of them open around 30 psi). I had some heat issued on the 2nd floor last winter.
Why is there no water in the 2nd loop?
Was purging system of air after I replaced the pump.
Here are some pictures



1. I manually opened 1 zone valve and closed the 2nd zone. Purged the system and refilled the 1st system. Used an external pressure guage to check the pressure through the hose faucet. Pressurized the system to 15 psi.
2. Shutoff the 1st zone and opened the 2nd zone. No water drains from the system. Adding water just increases the pressure reading from the boiler. I didn't go above 20 because I feared the pressure relief valve would open. (I'm assuming most of them open around 30 psi). I had some heat issued on the 2nd floor last winter.
Why is there no water in the 2nd loop?
#2
I need to understand a little bit more about the piping.
I think that what you were doing is pushing the water through the boiler, up through the open zone valve, and out the drain. It had no reason to go up and through the zone... it followed the path of least resistance.
Where does the water enter the boiler from the domestic piping? Is it the pipe with the yellow tag on it? And that comes down and feeds into where? (not clear in photos)
It appears to me as if the installer has those two valves, the shutoff and the drain, reversed in position on each of the returns.
Based on what I THINK I can see in the photos, the water goes into the boiler on that pipe that goes to the relief valve and the expansion tank, and into the top of the boiler.
MAKE CERTAIN that the boiler is COOL... below 100F ... before you purge! You'll possibly crack the boiler if you don't... you don't want your boiler on crack... let alone m3th.
Hook up the drain hose to the drain valve for the zone ... but LEAVE THE ZONE VALVE CLOSED.
The water will go up and through the zone and out the drain.
Opening the zone valve allows the water to take the 'shortcut'.
Open the drain and feed water in to push the air out of the pipe and fill with water. You might want to repeat this for each of the zones.
I think that what you were doing is pushing the water through the boiler, up through the open zone valve, and out the drain. It had no reason to go up and through the zone... it followed the path of least resistance.
Where does the water enter the boiler from the domestic piping? Is it the pipe with the yellow tag on it? And that comes down and feeds into where? (not clear in photos)
It appears to me as if the installer has those two valves, the shutoff and the drain, reversed in position on each of the returns.
Based on what I THINK I can see in the photos, the water goes into the boiler on that pipe that goes to the relief valve and the expansion tank, and into the top of the boiler.
MAKE CERTAIN that the boiler is COOL... below 100F ... before you purge! You'll possibly crack the boiler if you don't... you don't want your boiler on crack... let alone m3th.
Hook up the drain hose to the drain valve for the zone ... but LEAVE THE ZONE VALVE CLOSED.
The water will go up and through the zone and out the drain.
Opening the zone valve allows the water to take the 'shortcut'.
Open the drain and feed water in to push the air out of the pipe and fill with water. You might want to repeat this for each of the zones.
#3
Member
Thread Starter
Join Date: Oct 2013
Posts: 43
Received 0 Votes
on
0 Posts
Yeah, the piping has a lot to be desired. The air vent is located right above where the water enters the boiler. The basement and 1st fl are on the same zone, so you can imagine the heat loss from an unfinished basement.
I've edited the pictures to make it more clear - at least I hope so.
Btw, it's m3ath3ad not m3thead, ( some jerk took "meathead") although I might have to "break bad" to pay for the system to re-zoned and re-piped
Is it normal to have the pump flow into the boiler and not away from the boiler?


I've edited the pictures to make it more clear - at least I hope so.
Btw, it's m3ath3ad not m3thead, ( some jerk took "meathead") although I might have to "break bad" to pay for the system to re-zoned and re-piped
Is it normal to have the pump flow into the boiler and not away from the boiler?



#4
you can imagine the heat loss from an unfinished basement.
Btw, it's m3ath3ad not m3thead
I've edited the pictures to make it more clear - at least I hope so.
So then, as I said, leave both of the zone valves CLOSED. This will 'detour' the water up through the zone and out the drain.
Is it normal to have the pump flow into the boiler and not away from the boiler?
#5
Member
Thread Starter
Join Date: Oct 2013
Posts: 43
Received 0 Votes
on
0 Posts
Confused - 2nd Zone Heats up but no pressure reading on external pressure gauge
I'm the guy who had thought he had no flow on his 2nd zone. I never got water to flow out of my 2nd zone drain valve or had any pressure. So I wanted to see if the zone would get hot anyways. I turned on the thermostat and all the baseboards are getting hot, I can hear the pump circulating. So the first baseboard gets hot, the last baseboard gets hot, the return pipe gets hot.
Could the shutoff to the drain be broken and staying closed even though the handle turns?
Are the the little handles on the zone valve supposed to move left when the zone calls for heat or is that just for manual manipulation?
This zone is the farthest left in picture
Could the shutoff to the drain be broken and staying closed even though the handle turns?
Are the the little handles on the zone valve supposed to move left when the zone calls for heat or is that just for manual manipulation?
This zone is the farthest left in picture

#6
Hi M3at!
I might tack this onto the end of your other thread.
I suppose anything is possible...
No, they won't move when the valve automatically opens/closes, but you CAN use them to tell if the valve is actually open or closed.
If the handle moves freely with no resistance at all... just flopping in the breeze, the valve is OPEN.
If it takes pressure to move the handle and you hear the gears 'whirring', the valve is CLOSED.
Your title says 'external gauge shows no pressure'... but there's nothing in your message to explain that. Tell us where you had the gauge connected.
Should be darn near silent... do you mean that you hear the water gushing and gurgling through the pipes? If so, that ain't right.
I might tack this onto the end of your other thread.
Could the shutoff to the drain be broken and staying closed even though the handle turns?
Are the the little handles on the zone valve supposed to move left when the zone calls for heat or is that just for manual manipulation?
If the handle moves freely with no resistance at all... just flopping in the breeze, the valve is OPEN.
If it takes pressure to move the handle and you hear the gears 'whirring', the valve is CLOSED.
Your title says 'external gauge shows no pressure'... but there's nothing in your message to explain that. Tell us where you had the gauge connected.
I can hear the pump circulating
#8
Member
Thread Starter
Join Date: Oct 2013
Posts: 43
Received 0 Votes
on
0 Posts
I tried purging but nothing came out the pressure just climbed.
I attached the external gauge to the other zone drain and the boiler drain to double check the boiler gauges.
The pump was near silent the sound was whisper quiet not the sound of water rushing through.
I attached the external gauge to the other zone drain and the boiler drain to double check the boiler gauges.
The pump was near silent the sound was whisper quiet not the sound of water rushing through.
#9
I tried purging but nothing came out the pressure just climbed.
You have the valve handle ABOVE the drain OPEN, correct?
I attached the external gauge to the other zone drain and the boiler drain to double check the boiler gauges.