Gas boiler pressure too high

Hi, I have a very old gas boiler (50 plus years) with a steel expansion tank. I had a backflow preventer installed in May as there was not one at all. The PRV leaks occasionally when the pressure on my boiler reaches 30psi. I called the plumber and he drained the expansion tank. One week later it is leaking again. The pressure only rises when the unit is called for heat. #1 Do I need a new expansion tank? #2 could the back flow preventer have anything to do with this? #3 is there anything else that could cause the pressure to rise so high? thanks for your help.
 
Sponsored Links
  #2  
Old 12-11-13, 10:14 AM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,964
Received 37 Votes on 32 Posts
Possibly the fill valve is leaking... But the pressure would be hi all the time and just continue to rise until the relief valve trips...

The expansion tank needs to be emptied completely... Possibly the tech did not do this... This is probably the cause. Often it may seem like the tank is empty, when indeed it is not...

Call him back.. You paid for a service and you still have issues... He should correct it....

Pics of the boiler will help....
 
  #3  
Old 12-11-13, 01:27 PM
Member
Thread Starter
Join Date: Dec 2013
Posts: 3
Received 0 Votes on 0 Posts
tech came back and drained the tank again. lots of particles came out toward the end. he turned off the feed valve and said that if the pressure rises again then the expansion tank has a leak. when we bought the house we noticed that the expansion tank had a towel and plastic wrapped around the valve. if it has a leak would that cause the pressure to rise in the boiler?
 
  #4  
Old 12-11-13, 01:36 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,964
Received 37 Votes on 32 Posts
You would see water if there was a leak....
 
  #5  
Old 12-11-13, 01:53 PM
Member
Thread Starter
Join Date: Dec 2013
Posts: 3
Received 0 Votes on 0 Posts
that's what i thought. is it safe to have the feed valve off? there will be no more new water feeding into the boiler, correct? thanks for your time.
 
  #6  
Old 12-11-13, 02:35 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,964
Received 37 Votes on 32 Posts
is it safe to have the feed valve off? there will be no more new water feeding into the boiler, correct?
Yes and yes.... And with the valve off and if there was a leak you would have 0 psi in a short amount of time....

Starting cold pressure should be 12-15 psi...
 
  #7  
Old 12-11-13, 05:20 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
is it safe to have the feed valve off?
if there was a leak you would have 0 psi in a short amount of time....
So with that valve turned off it's very important to keep a close watch on the pressure gauge.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: