Pressure relief valve won't stop dumping water

So a few days ago I checked on the boiler and it was pinned at 0psi but the system was still heating fine. But I feared burning out the pump so I went ahead and filled the system with a little more water until it hit 12psi. I didn't add a TON of water or anything. The boiler was not running at the time.

After running it spewed up a good amount of water (figured I overfilled a little). However it's kept spewing out water over the past couple of days! Right now the system is off and at 19psi but the 30psi relief valve is still dripping water at a constant rate. The valve is rather new (got it a little over a year ago). I'm guessing the valve is bad already since it's leaking at 19psi which it shouldn't. I also just had a new expansion tank put in but have no idea how that works really lol.
Just frustrating because obviously the 0 psi it was at was not good, so I filled it and now I have problems. Should I have left it? ugh lol
Any advice would be great thanks.
 
Sponsored Links
  #2  
Old 12-13-13, 12:54 PM
Member
Join Date: Jun 2012
Posts: 917
Received 3 Votes on 3 Posts
It could be that your gauge is off. See the thread at the top of this forum on how to verify your boilers pressure gauge.

http://www.doityourself.com/forum/bo...ure-gauge.html
 

Last edited by NJT; 12-13-13 at 03:39 PM. Reason: you guys need to learn how to copy and paste links!
  #3  
Old 12-13-13, 03:23 PM
Member
Join Date: Dec 2010
Location: USA
Posts: 182
Received 0 Votes on 0 Posts
Yes I just made another gauge (lost the other one) yesterday to check my pressures. Cost about $10 to make. Just need a hose bib to 3/4 pipe thread adapter, a plug with a hole on top for gauge and a gauge. Screw them all together and screw into hose bib and check. Granted my $4 gauge was a few PSI off from my boiler gauge, but it lets you know you are in the ballpark. Verify the gauge and check bad. Yes the valve can be bad or have some crap under the seat, but there has to be a reason for the pressure loss and initial blow off.
 
  #4  
Old 12-13-13, 03:33 PM
Member
Join Date: Oct 2013
Location: United States
Posts: 2,758
Received 21 Votes on 20 Posts
I would trust the relief valve before the gauge.
It's possible the gauge went bad and instead of going from 0-12 you went from 19-30.
Maybe there never really was a pressure drop, just a bad gauge.
 
  #5  
Old 12-13-13, 03:45 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
All the guys are right... the pressure gauges that are supplied with boilers are the cheapest pieces of dookie they can get. They are almost ALWAYS bad.

In the interest of SAFETY, as Spott has said, NEVER ASSUME that the relief valve is the culprit. ALWAYS err on the side of caution!

If there's ever any question whether the relief or the gauge is bad, TRUST HISTORY... ALWAYS suspect the gauge is bad. History was invented for a reason! So that we don't continue to make the same mistakes... over and over and over ...

Read this one also:

http://www.doityourself.com/forum/bo...sion-tank.html

The step-by-step instructions in that thread explain how to properly check and charge the air on an expansion tank, and this should be done at LEAST every two years, preferably ANNUALLY.
 
  #6  
Old 12-13-13, 04:23 PM
Member
Join Date: Sep 2008
Location: Long Island
Posts: 769
Received 0 Votes on 0 Posts
system should be 12psi cold auto feed then when I runs right after it satisfies the stat tops 20psi the relief is doing it's job pressure reading is wacked...you can't over fill a hot water baseboard system just over pressurize it..drain the expansion tank on next cycle off water has no place to expand if it is full
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: