Installing a boiler feed valve question

Reply

  #1  
Old 01-09-14, 02:06 PM
Member
Thread Starter
Join Date: Oct 2013
Posts: 39
Received 0 Votes on 0 Posts
Installing a boiler feed valve question

Thinking of adding a boiler feed valve on my system. My piping has a shutoff valve followed by a backflow preventer and then another shutoff valve.

I know I need to install it after the backflow preventer but should I install it before or after the last shutoff valve.
 
Sponsored Links
  #2  
Old 01-09-14, 02:39 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 2 Votes on 2 Posts
I know I need to install it after the backflow preventer but should I install it before or after the last shutoff valve.
BEFORE. That will allow you to service the valve easily.

Before installing any new valves on the water feed line, FLUSH THE LINE UNDER FULL FLOW by rigging up a hose connection to the line and turning it on FULL BLAST to loosen the 'crud' that builds up in little used piping from domestic to boiler.

I like to add a 'flush valve' ahead of the valves for this purpose:



Drain/flush valve on the right. I hook hose to it periodically and flush a few gallons out. I'm on a private well and not chlorinated, so I have more than one reason to flush that 10' line between the boiler and the main line... don't want no creepy crawlies breeding in a plumbing 'dead end'.

The next item to the left of the drain is a 'WYE strainer' which now has a small valve on it for periodic flushing of the screen inside of it.

So, in order from the domestic to the boiler:

domestic->ball valve->drain/flush->wye strainer->backflow prev->reducing valve->ball valve->boiler

You don't really see the last ball valve in the picture because it's incorporated in the Watts RBFF expansion tank fitting (which is a real neat deal which AFAIK I invented and Watts owes me royalty checks for!) Since you don't have the RBFF, substitute a ball valve.

One other use for that drain ahead of the feed chain ... notice that the RBFF also has a drain on it, just behind the gauge. If my feed valve ever gets plugged or I want a FAST flush, I can connect a wash machine hose between the two and bypass the feed chain.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: