Pressure Relief Valve Leaking

Hello

I changed my pressure relief valve yesterday because the my pressure guage was indicating that the pressure was not being kept. When I replaced the relief valve, water continues to consistently spill. The spill is not a little, but a lot of hot water. What am I missing? Because of this I am not getting hot water or enough hot water to the house and also is affecting my heating. Please need urgent help.
 
Sponsored Links
  #2  
Old 01-19-14, 05:56 AM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,809
Received 14 Votes on 12 Posts
Is this from your boiler or HWH?

Please post make and models...

Its either too much water in the boiler from a faulty fill valve or a faulty expansion tank... ( If boiler).

Can you post pictures?

Oh and welcome to the forums...

Read here...

http://www.doityourself.com/forum/bo...sion-tank.html
 
  #3  
Old 01-19-14, 06:05 AM
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 7
Received 0 Votes on 0 Posts
Hey Lawrosa

I don't know much about this stuff, but I would have to say the hot water heater (not the 40 gallon tank). The Make is Williamson, Model - GWI - 063N-1

Just a brief history, I had a similar issue 1 yr ago and replaced the pressure relief valve. It worked with some spillage (sometime a constant stream and other times just dripping), which I could have lived with. When I noticed the similar signs yesterday, I immediately thought of that being the issue. When I removed it, there were a lot of gunk in the valve and after cleaning it, I tested it with water. No suprise, the water leaked right out.

I placed a new valve last night, but its spitting out even more. What am i missing and what could be causing the issue.

Thanks for any insight.
 
  #4  
Old 01-19-14, 06:09 AM
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 7
Received 0 Votes on 0 Posts
I also purchased a cleaning fluid from home depot to place into the boiler to get the gunk out. i poured that in last night as well.
 
  #5  
Old 01-19-14, 06:16 AM
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 7
Received 0 Votes on 0 Posts
lastly, I have noticed that the pressure is consistently at 40 psi. Is that normal?
 
  #6  
Old 01-19-14, 06:19 AM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,809
Received 14 Votes on 12 Posts
Is this for your heat or hot water????

This is the model you gave me.. Its a boiler... Please be more specific...

GWI - Gas Water Induced-Draft | Williamson | Product Detail
 
  #7  
Old 01-19-14, 07:03 AM
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 7
Received 0 Votes on 0 Posts
The issue is occurring on the boiler - as stated in my original post.

Thank You
 
  #8  
Old 01-19-14, 07:07 AM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,809
Received 14 Votes on 12 Posts
First step is to service the expansion tank.. Thats the most probably cause...

Did you read that link?

What does the pressure and temp gauge read on the boiler???
 
  #9  
Old 01-19-14, 08:53 AM
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 7
Received 0 Votes on 0 Posts
I did read the link and honestly its a bit over my head....

the gauge reads as follows 40psi, and 120
 
  #10  
Old 01-19-14, 09:45 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 2 Votes on 2 Posts
It that's over your head then it's time to get out the phone book and make some phone calls.
 
  #11  
Old 01-19-14, 11:05 AM
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 7
Received 0 Votes on 0 Posts
I actually figured out the issue. The fill regulator is faulty causing water to continuously feed the boiler. This is causing the relief valve to constantly release. I am in the process of testing the expansion tank, but would most likely replace it... but thanks for the help
 
  #12  
Old 01-19-14, 11:46 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 2 Votes on 2 Posts
I actually figured out the issue
So with a little effort you realized that it's NOT over your head, didn't you?

As long as you do due diligence and keep your eye on the pressure gauge to make sure it doesn't go too low, there's no reason why you can't put off replacing it until the spring.

Heating system is CLOSED and should not lose water. (if it does, it indicates a slow leak somewhere)

You would most likely be fine if you pressurized the system to 12-15 PSI when the boiler is COLD and CLOSE THE MANUAL SHUTOFF valve.

It is perfectly OK to run the boiler with that valve closed.

AS LONG AS YOU KEEP YOUR EYE ON THE GAUGE!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: