Psi question

Had new boilermate indirect hot water tank installed today (under warrenty). Also installed new expansion tank. My gauge on furnace is now reading 20psi. prior to install, the reading was consistently 12-15 psi. Is this ok or do i need to call plumber back to correct something? Thanks.
 
Sponsored Links
  #2  
Old 02-25-14, 03:23 PM
Member
Join Date: Dec 2010
Location: USA
Posts: 172
20 at what temp? Mine runs about 20 psi hot 180* and 15 psi cold below 100*

12 to 15 should be a minimum cold fill pressure
 
  #3  
Old 02-25-14, 03:25 PM
Member
Thread Starter
Join Date: Feb 2014
Location: usa
Posts: 12
looks like the boiler is set at 120.
 
  #4  
Old 02-25-14, 03:32 PM
Member
Thread Starter
Join Date: Feb 2014
Location: usa
Posts: 12
I think i answered incorrectly. The tank is set for 120, but the gauge reads 20 psi and 180*. but stays at 20psi even when oil furnace is not firing
 
  #5  
Old 02-25-14, 03:38 PM
Member
Thread Starter
Join Date: Feb 2014
Location: usa
Posts: 12
one more update. It now is reading about 23psi at 190*. thoughts?
 
  #6  
Old 02-25-14, 03:51 PM
Member
Thread Starter
Join Date: Feb 2014
Location: usa
Posts: 12
looks like 20 psi at 180* and 22 psi at 195*. seems to stay at 20psi even when furnace is not firing
 
  #7  
Old 02-25-14, 03:56 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Likes Received: 1
Why is the temperature going up to 195 ? There's most likely no need for that and saving to be had if turned down.

looks like 20 psi at 180* and 22 psi at 195*
That's FINE for that temperature.

seems to stay at 20psi even when furnace is not firing
"Not firing" is meaningless... it's the TEMPERATURE in the boiler that determines the pressure.

What is the pressure when the boiler is under 100F ?

What you SHOULD see is 12-15 PSI when the boiler is COLD... and perhaps as much as 8-10 PSI HIGHER when HOT.

Find the temperature control on the boiler and tell use what that is set to.
 
  #8  
Old 02-25-14, 03:58 PM
Member
Thread Starter
Join Date: Feb 2014
Location: usa
Posts: 12
the boiler is set to 120*
 
  #9  
Old 02-25-14, 03:58 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Likes Received: 1
No, I don't think so.

The INDIRECT is set to 120.

The BOILER has it's own temperature setting.
 
  #10  
Old 02-25-14, 04:01 PM
Member
Thread Starter
Join Date: Feb 2014
Location: usa
Posts: 12
ahhh. correct. looks like the boiler is set at 160* low and 175* high with 15* diff.
 
  #11  
Old 02-25-14, 04:41 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Likes Received: 1
You've got an L8124 aquastat? AND an indirect water heater? Why?

the boiler is set at 160* low and 175* high with 15* diff.
Something ain't jiving here.

Time for some history...

Tell us the make and model of the boiler.

Does your boiler have a tankless coil in it that was abandoned when you got the indirect? If so, the aquastat should have either been modified to a 'cold start', or replaced with a 'cold start' model.

There is NO REASON at all for the LOW to be set at 160! You are WASTING FUEL! Besides that, it's printed right on the front of the white block inside the aquastat that the LOW and HIGH should never be closer than 20 apart.

Turn the LOW down to 120 and the DIFF to 10 for starters and save yourself a good deal of fuel $

Leave the HIGH at 175 for now.

With the HIGH at 175 it doesn't explain why the boiler is going to 195 though... or your thermometer is wrong.

Why don't you take some pics in addition to answers for the above questions...
 