Zone valves 2 wire vs 4 wire

I've installed a multi-zone hydronic heating system and I've noticed that some zone valves have 2 leads and some have 4 leads. I understand that the ones with 4 leads have a pair for the aqua-stat of my boiler.

1. Is there a way to use the 2-wire type to also tie to aquastat?
2. If I can't tie to aquastat, what is the disadvantage of only connecting to the thermostats for these zones fed off from 2-wire valves?
 
Sponsored Links
  #2  
Old 03-27-14, 07:30 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 2 Votes on 2 Posts
Shawn, give us more details...

Tell us the make/model of the valves for starters.
 
  #3  
Old 03-29-14, 05:04 PM
Member
Thread Starter
Join Date: Nov 2013
Posts: 26
Received 0 Votes on 0 Posts
Thanks for the interest NJ Trooper.

I have loked a bit further, and realized my post is wrong. I should have referred to the endswitch, no the aquastat.

I have Honeywell zone valves.

V8043A has 2 leads for the thermostat only.

V8043E has 2 leads of the thermostat and 2 leads for the endswitch.

The problem I have is that I have installed some V8043A on my system now. I know I can signal from the thermostat to the zone valve to open, but I am not sure how I can send the call signal to the burner relays.

Thanks!

Shawn
 
  #4  
Old 03-29-14, 05:38 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 2 Votes on 2 Posts
The problem I have is that I have installed some V8043A on my system now. I know I can signal from the thermostat to the zone valve to open, but I am not sure how I can send the call signal to the burner relays.
Well... you can't...

You need an ISOLATED switch to connect to the boiler to fire it up.

I believe that the BODY of the valve is the same between the A and the E valves, so you could purchase some E heads for the A valves.

OR, you could pick up a Taco ZVC panel and jumper the endswitch connections in the panel.
 
  #5  
Old 03-29-14, 05:41 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,799
Received 10 Votes on 8 Posts
V8043A has 2 leads for the thermostat only.
They are used for constant circulation and boiler firing off high limit. Like in an apartment where the t stat only opens the zone....
 
  #6  
Old 03-29-14, 05:54 PM
Member
Thread Starter
Join Date: Nov 2013
Posts: 26
Received 0 Votes on 0 Posts
I see. Thanks for the help.

I cannot just include the call to the boiler circuit in the t-stat to motor circuit, and signal all at once?

Or, could I install a relay in a box and use that to switch to call to the boiler?

I suppose as long as these couple zones could be left to just respond to the thermostat, and the boiler will kick on when other zones call for heat, to keep water temperature up in the boiler. Maybe an option. They might circulate cooler water some of the time...
 
  #7  
Old 03-29-14, 05:56 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 2 Votes on 2 Posts
I cannot just include the call to the boiler circuit in the t-stat to motor circuit, and signal all at once?
No, you'll fry either or both the 24V transformer for the zone valves, or the transformer in the aquastat. You would be connecting two powered circuits together and those transformers will cook.

Or, could I install a relay in a box and use that to switch to call to the boiler?
That's what the Taco ZVC panel would do for you.
 
  #8  
Old 03-29-14, 06:06 PM
Member
Thread Starter
Join Date: Nov 2013
Posts: 26
Received 0 Votes on 0 Posts
This is good information.

So I can install a metal box adjacent the zone valve and put a relay in it and run the relay off the thermostat circuit to the zone valve? Then, I can run off the relay into the circuit that signals the boiler (TT) along with the other V8043E already connected. Therefore, the relay is only a switch to open and close the TT circuit and won't add voltage. Is that right?

Thanks so much!
 
  #9  
Old 03-29-14, 06:16 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 2 Votes on 2 Posts
Yes, you could do that with a DOUBLE POLE relay that has a 24VAC coil.

Actually, you could use a SINGLE pole relay and wire the COIL of the relay in parallel with the MOTOR leads of the zone valve. When the thermostat calls, it will energize both the relay and the zone valve.

Problem with this is you might need a larger transformer to power the extra load.

How many zone valves total do you have?

How many VA is your 24V transformer?
 
  #10  
Old 03-29-14, 06:18 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 2 Votes on 2 Posts
  #11  
Old 03-29-14, 06:29 PM
Member
Thread Starter
Join Date: Nov 2013
Posts: 26
Received 0 Votes on 0 Posts
I have multiple transformers and zone valves.

Transformers output 24 Vac at 40 VA and I understand that 3 max valves per transformer is allowed.

So, we are saying that if I do 2 ZV per transformer then I can use single pole? If I stick with 3 ZV per TX then use double?

Thanks!
 
  #12  
Old 03-29-14, 06:47 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 2 Votes on 2 Posts
It depends on what the added relays are going to draw. Probably not as much as a zone valve, I would think you could still do 3 valves per transformer.

Are you dismissing the ZVC panel for some reason? It really is the cleanest, easiest, and probably by the time you get done purchasing boxes and relays and all that other junk, the cheapest.
 
  #13  
Old 03-29-14, 06:54 PM
Member
Thread Starter
Join Date: Nov 2013
Posts: 26
Received 0 Votes on 0 Posts
I see single pole relays for 6$ for fan switching and I would only use them for 2 ZVs and I have the other parts around. So i would save by not spending the 100$ on the switch box. And I like the challenge of it I guess - learning.

I will probably trial the system without the relays to see if the rooms are still comfortable from the boiler water staying hot from other valves calling. You have been very helpful and I have a better understanding now for sure. Thank you for the help.
 
  #14  
Old 03-29-14, 07:19 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 2 Votes on 2 Posts
I like the challenge of it I guess - learning.
No problem with that!

Let us know how it works out.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: