no heat downstair, but upstairs good, gas boiler, baseboard heat. themos fine


  #1  
Old 04-03-14, 12:48 PM
D
Member
Thread Starter
Join Date: Apr 2014
Location: USA
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
no heat downstair, but upstairs good, gas boiler, baseboard heat. themos fine

Hi:

Have a Weil-McLain Gas Boiler CGi cast iron boiler with 3 zone baseboard heat, 3 separate thermostats and Honeywell zone valves (similar to V8043). The system was working fine for a year.

Now a problem: Zone 1 upstairs works fine (has separate thermostat gas boiler turns on and heats fine. Zone 2 and 3 downstairs with separate themostats turn on, but gas boiler does not ignite. I switched all thermostats and they are all working fine, The valves move when I call for heat for Zone 2 and Zone 3, looks like the flu opens, but boiler never ignites. It ignites when I put upstairs Zone 1 on (and I can heat up downstairs like that) but wanted to solve the problem.

I think the thermos work, zone valves work, good pressure in system. Problem lies with no ignite for Zone 2 and 3 but ignites for Zone 1.

What parts should I buy or replace (should I jump wires). Thanks.
Regards
Daren
 
  #2  
Old 04-03-14, 01:09 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Honeywell zone valves (similar to V8043).
Similar or not, we would like to know what they ARE, please post the model number of the zone valves.

A thermostat can work and open the zone valve, but the 'endswitch' in the zone valve that tells the boiler to fire can be bad and the boiler won't fire.
 
  #3  
Old 04-03-14, 01:15 PM
S
Member
Join Date: Oct 2013
Location: United States
Posts: 2,768
Received 141 Upvotes on 133 Posts
Darin,
Your zone valve has 4 terminals. Two wires come from the t-stat and open the valve, the other two go to the boiler to fire it up on a call for heat. Since they open your t-stat circuit is fine. Find the point where the two wires from each valve go to TT on the boiler. It will be the same location that zone 1 is tied into.
You may just have a loose connection.

I doubt if it's serious since Z1 is working and 2 & 3 have the same issue. If you find the bad connection you'll find the problem. Redo the wires if that's the case and you'll be fine.

Good Luck,
 
 