Weil Mclain Gold CGA apparent pressure relief valve problem.

I find a puddle of water under where the pressure relief valve is on my boiler. I thought that the boiler temp was to high so I dropped the set point down 10 deg. I still have the water showing up on the floor. Is this a poor relief valve and or auto fill valve or something else?
 
Sponsored Links
  #2  
Old 04-05-14, 06:40 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,892
Received 25 Votes on 23 Posts
could be fill valve a expansion tank heeds sevicing...

Whats the psi read on the boiler gauge?

Read the stickys regarding the expansion tank at the top of this forum...

Let us know and welcome....
 
  #3  
Old 04-05-14, 07:07 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
Making it easy for you, links here:

http://www.doityourself.com/forum/bo...sion-tank.html

Always a good idea to verify pressure gauge as well:

http://www.doityourself.com/forum/bo...ure-gauge.html
 
  #4  
Old 04-06-14, 04:17 PM
Member
Thread Starter
Join Date: Apr 2014
Location: United States
Posts: 2
Received 0 Votes on 0 Posts
Weil McLain Gold CGA issue

I looked at the system and can say without a doubt that the tank was never checked or re-charged. So I am going to follow the procedure and install the valve for testing and then either replace the tank and add the correct pressure or just put the proper pressure in the existing one. The existing one is 12 years old, should I just replace it or should it be ok to just charge it especially since I am installing the test valve? Thank you for your input.
 
  #5  
Old 04-06-14, 05:32 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
At 12 years old, I would probably just replace.

Be aware that there are tanks for heating systems, and tanks for potable water systems. Make sure to get the right type even if the guy at HD tells you they're all the same... they're not really. And replace with same size of course.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: