Troubleshooting boiler noise
#41
In fact I find air scoops not to work as well from my experience.
The garage loop leaked before lived here and the previous owner did virtually nothing about it (not sure how long).
Mine was installed in 08 so it's either overdue or a matter of time before it needs done......My tank is a Honeywell TK300-30-1 by the way, any recommendations on a new one?
IMHO, they're all basically the same... but stick with a name brand.
Are these genuinely adequate, or maybe phrased a different way, as good as an air scoop or spirovent?
My system also has radiator vents as shown in the picture below, which I'm sure are all crusted up inside and non-functioning...likely installed in '57 when my house was built.
#43
Member
Join Date: Dec 2013
Location: USA
Posts: 228
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I've been contemplating putting a water softener in my house, if a drain and refill is required, would it be worth installing the water softener beforehand?
Determine if water treatment is needed.
If not a water softener then running the system with a LWCO and the feed valve closed would be good.
#44
You need to know what is in your water first. Do a search to see if your city has a water quality report.
Determine if water treatment is needed.
If not a water softener then running the system with a LWCO and the feed valve closed would be good.
Determine if water treatment is needed.
If not a water softener then running the system with a LWCO and the feed valve closed would be good.
http://www.eastmoline.com/documentcenter/view/4172
I do not see where it lists water hardness, but I did try the method with the colored paper strips. It came out to just under 7.0 gpg, so I was still riding the fence on installing a softener, but opted not to at this point. I will start looking for info on Low Water Cutoff's as well.
#45
Member
Join Date: Mar 2015
Location: USA
Posts: 17
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Boiler Noise
Chacho
I would place the Webstone drain valve between the 1/2" tee and the 1/2" female adapter. Be sure and support the 1/2" line and tank by the larger pipes above it.
Make sure that the tank pressure and the pressure reducing valve is set to 15psi.
Unless the tank gets water logged, there is no need to replace it, but if you want to replace it, buy an Amtrol Extrol #30. Supplyhouse.com
If you want to replace the air vent on the air scoop, I like the Taco Hi-Vent air vent. You just have to make sure the thread size is correct. Probably 1/4" NPT?
To test it press the schrader valve and see if water squirts out and when released the flow stops. If it continues to drip replace it. If you are going to drain the sys down then replace it, anyway, it is cheap and you won't have deal with the problems later.
Chacho, the small coin vent in your baseboard comes in two flavors, A manual vent that you open with a small screwdriver until a stream of water exits the vent, which you then screw closed and a Hydroscopic coin vent. The Hydroscopic coin vent has wafers in it that expand when in contact with water and the expansion of the wafers shuts off the flow. These are normally in the open position. They can be mechanically closed with a screwdriver. These vent let the air entrapped in the high points of the circuit out so the water can fill the pipe.
lawrosa
Just manufacturers preference, of course, they never want to warrant a tank with a free replacement. There are 4 kinds of tanks on the market: Hydronic, Potable, Solar, and Radiant. Hydronic is for a closed hydronic system, Potable is for your water heater (an open system), Solar is for the high temp in solar applications, and Radiant for a system that uses radiant infloor pex, barrier or non barrier, tubing with anti freeze.
I believe that the Hydronic (Extrol) doesn't have a coating to prevent rust on the inside of the tank from the trapped air. That is why orientation recommendation is specified by some companies, to keep trapped air out of the tank.
Potable, Solar, and Radiant tanks have a barriers inside to handle corrosion and chemical corrosion so that the tank doesn't rust out.
Eventually, trapped air is absorbed by the water and expelled by the air elimination device.
I would place the Webstone drain valve between the 1/2" tee and the 1/2" female adapter. Be sure and support the 1/2" line and tank by the larger pipes above it.
Make sure that the tank pressure and the pressure reducing valve is set to 15psi.
Unless the tank gets water logged, there is no need to replace it, but if you want to replace it, buy an Amtrol Extrol #30. Supplyhouse.com
If you want to replace the air vent on the air scoop, I like the Taco Hi-Vent air vent. You just have to make sure the thread size is correct. Probably 1/4" NPT?
To test it press the schrader valve and see if water squirts out and when released the flow stops. If it continues to drip replace it. If you are going to drain the sys down then replace it, anyway, it is cheap and you won't have deal with the problems later.
Chacho, the small coin vent in your baseboard comes in two flavors, A manual vent that you open with a small screwdriver until a stream of water exits the vent, which you then screw closed and a Hydroscopic coin vent. The Hydroscopic coin vent has wafers in it that expand when in contact with water and the expansion of the wafers shuts off the flow. These are normally in the open position. They can be mechanically closed with a screwdriver. These vent let the air entrapped in the high points of the circuit out so the water can fill the pipe.
lawrosa
Just manufacturers preference, of course, they never want to warrant a tank with a free replacement. There are 4 kinds of tanks on the market: Hydronic, Potable, Solar, and Radiant. Hydronic is for a closed hydronic system, Potable is for your water heater (an open system), Solar is for the high temp in solar applications, and Radiant for a system that uses radiant infloor pex, barrier or non barrier, tubing with anti freeze.
I believe that the Hydronic (Extrol) doesn't have a coating to prevent rust on the inside of the tank from the trapped air. That is why orientation recommendation is specified by some companies, to keep trapped air out of the tank.
Potable, Solar, and Radiant tanks have a barriers inside to handle corrosion and chemical corrosion so that the tank doesn't rust out.
Eventually, trapped air is absorbed by the water and expelled by the air elimination device.
#46
Member
Join Date: Mar 2015
Location: USA
Posts: 17
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Boiler Noise
Chacho
If you had well water instead of Mississippi river water I would be more concerned.
I don't see in any of your photos an indication of scaling. Does you toilet bowl have calcified ring around it where the water level is? See any white streaking where the sprinklers splash against the house? Any white scaling around the handles of the faucets in your house?
Before I would buy or install a water softener, I would fill the system with distilled water that you can buy from Walmart for a buck a gallon. Which I use all the time.
If you had well water instead of Mississippi river water I would be more concerned.
I don't see in any of your photos an indication of scaling. Does you toilet bowl have calcified ring around it where the water level is? See any white streaking where the sprinklers splash against the house? Any white scaling around the handles of the faucets in your house?
Before I would buy or install a water softener, I would fill the system with distilled water that you can buy from Walmart for a buck a gallon. Which I use all the time.
#47
Even with only moderately hard water, if there is a leak for unknown long period of time that goes unrepaired, the fact that water is feeding constantly, even at a slow rate, will eventually concentrate the minerals to the point that they cause problems.
When the water is heated, the minerals precipitate. That's the reason that the 'thankless coils' that are in the boiler that some ppl use to make domestic hot water get limed up. Even with only slightly hard water, over time, this will happen.
A ring in a terlet bowl would only occur in cases of EXTREME water hardness. That's no indication of what can occur in a LEAKY boiler system that has constantly fed small amounts of water for an unknown amount of time.
7 gpg is not terribly hard, I would call that the high end of 'moderate' myself. My well water is about 8 gpg, after the softener, about 3.
When the water is heated, the minerals precipitate. That's the reason that the 'thankless coils' that are in the boiler that some ppl use to make domestic hot water get limed up. Even with only slightly hard water, over time, this will happen.
A ring in a terlet bowl would only occur in cases of EXTREME water hardness. That's no indication of what can occur in a LEAKY boiler system that has constantly fed small amounts of water for an unknown amount of time.
7 gpg is not terribly hard, I would call that the high end of 'moderate' myself. My well water is about 8 gpg, after the softener, about 3.
#48
7 gpg is not terribly hard, I would call that the high end of 'moderate' myself. My well water is about 8 gpg, after the softener, about 3.
Softening causes the water to be more conductive... I would not do it...
Note my water was never softened till I moved in. My water heaters last less then 6 years... Ummm what am I doing to my boiler??? IDK but its still ticking...
#49
Maybe 7 is soft to you, but in the water treatment industry it's 'moderate'.
Anything under 3-4 is considered soft.
Don't know why you brought up conductivity? Electrolysis? No evidence of that here.
I've been softening the water here for 30+ years with no ill effects. My last water heater went about 20 years. The last boiler was installed in 84 and changed out in '12. Nothing wrong with it that was caused by softened water.
Anything under 3-4 is considered soft.
Don't know why you brought up conductivity? Electrolysis? No evidence of that here.
I've been softening the water here for 30+ years with no ill effects. My last water heater went about 20 years. The last boiler was installed in 84 and changed out in '12. Nothing wrong with it that was caused by softened water.
#50
Member
Join Date: Dec 2013
Location: USA
Posts: 228
Upvotes: 0
Received 0 Upvotes
on
0 Posts
"Minneapolis . . . softens water at a centralized softening plant."
The City of Moline: 2012 water report City of Moline, IL - Official Website
Both use surface water from the Mississippi.
Minneapolis yes. St. Paul NO. Moline yes. East Moline ? -no.-
See: Water Hardness [page 20 pdf]
"If You Can’t Beat It... Control It It is important to have an understanding of the factors that contribute to the overall corrosion rate when working with closed loop radiant floor heating systems." BY LANDON LEINWEBER, [PP 19-21 pdf] ModernHydronics May/June 2010.
"An Ounce Or So Of Prevention Keep boilers more efficient and corrosion free." BY Harvey Grodjesk,[ pp 16,18-20 pdf] Modern Hydronics Feb. 2013.
The City of Moline: 2012 water report City of Moline, IL - Official Website
" . . .Moline tap water is
softened at our water treatment plant
and its hardness (level of dissolved
minerals) is significantly lower than
the non-softened tap water in other
communities. . . .
softened at our water treatment plant
and its hardness (level of dissolved
minerals) is significantly lower than
the non-softened tap water in other
communities. . . .
Minneapolis yes. St. Paul NO. Moline yes. East Moline ? -no.-
See: Water Hardness [page 20 pdf]
"If You Can’t Beat It... Control It It is important to have an understanding of the factors that contribute to the overall corrosion rate when working with closed loop radiant floor heating systems." BY LANDON LEINWEBER, [PP 19-21 pdf] ModernHydronics May/June 2010.
Many in the industry believed that the act of artificially
softening water with a cation exchange softener caused
the water to become more corrosive. In fact, the opposite
has been found to be true and artificially softened water is
less corrosive than naturally soft water.[SUP]3,5[/SUP] In response to
this change, the U.S. Environmental Protection Agency (EPA)
and the American Water Works Association (AWWA) have
updated their literature to correct this misconception.[SUP]5[/SUP]
softening water with a cation exchange softener caused
the water to become more corrosive. In fact, the opposite
has been found to be true and artificially softened water is
less corrosive than naturally soft water.[SUP]3,5[/SUP] In response to
this change, the U.S. Environmental Protection Agency (EPA)
and the American Water Works Association (AWWA) have
updated their literature to correct this misconception.[SUP]5[/SUP]
"An Ounce Or So Of Prevention Keep boilers more efficient and corrosion free." BY Harvey Grodjesk,[ pp 16,18-20 pdf] Modern Hydronics Feb. 2013.
#51
While all that is true, CORROSION is not the same thing as MINERAL DEPOSITION.
And I say again:
If there was a leak in the system and the reducing valve was feeding water for unknown length of time, the mineral concentration in the boiler water can easily be high enough to deposit these minerals on the water side of the boiler.
And I say again:
If there was a leak in the system and the reducing valve was feeding water for unknown length of time, the mineral concentration in the boiler water can easily be high enough to deposit these minerals on the water side of the boiler.
#52
Member
Join Date: Mar 2015
Location: USA
Posts: 17
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Boiler Noise
Chacho
NJT is right. Corrosion is not the same as mineral deposition and the deposition of minerals precipitate out in the hottest part of the sys, that is the HX. Also, mineralization in the water does conduct electricity, which is harmful.
lawrosa is correct, ions circulating in softened water does increase electrical conductivity. Electrical currents in the water are detrimental to the rubber parts in the sys also corrosion between dis-similar metals.
Where I work the calcium in the water is 200 ppm. The guys here use it all time without a great deal of trouble. I have over the years, been using DI water or distilled water in my fill-ups, especially in anti-freeze or chemical applications.
As I remember, 1mm of deposits on the inside can reduce the heat transfer by 12%. If you think that that is a problem, Chacho, clean the sys this summer with Hercules Sizzle or a Rhomar product and flush the sys really well.
You must fix all the leaks. You can't have fresh water carrying oxygen into the sys. Oxygen corrodes the sys, anything cast iron.
But what about your boiler noise?
NJT is right. Corrosion is not the same as mineral deposition and the deposition of minerals precipitate out in the hottest part of the sys, that is the HX. Also, mineralization in the water does conduct electricity, which is harmful.
lawrosa is correct, ions circulating in softened water does increase electrical conductivity. Electrical currents in the water are detrimental to the rubber parts in the sys also corrosion between dis-similar metals.
Where I work the calcium in the water is 200 ppm. The guys here use it all time without a great deal of trouble. I have over the years, been using DI water or distilled water in my fill-ups, especially in anti-freeze or chemical applications.
As I remember, 1mm of deposits on the inside can reduce the heat transfer by 12%. If you think that that is a problem, Chacho, clean the sys this summer with Hercules Sizzle or a Rhomar product and flush the sys really well.
You must fix all the leaks. You can't have fresh water carrying oxygen into the sys. Oxygen corrodes the sys, anything cast iron.
But what about your boiler noise?
#53
Member
Join Date: Mar 2015
Location: USA
Posts: 17
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Boiler Noise
For those interested in water quality in hydronic sys.
Caleffi - Webinar Archive
and play this webinar Fluid Quality in
Hydronic Systems
with Guest Speaker Jeff Persons
Caleffi - Webinar Archive
and play this webinar Fluid Quality in
Hydronic Systems
with Guest Speaker Jeff Persons
#54
Member
Join Date: Mar 2015
Location: USA
Posts: 17
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Boiler Noise
For those interested in converting water hardness from one definition to another
link to this converter.
Cactus2000: Converter for hardness of water
link to this converter.
Cactus2000: Converter for hardness of water
#56
I just thought I would check back in with updates. I thought I would tackle the work on Sunday. I appreciate all the information on water quality and the impact of water on these systems. The website of webinars might be a curse because I'll probably be on that page for a long time!
I almost don't want to say this, fearing something will come up now, but after the changes, the boiler has never run quieter than it is right now. I wanted to post some pictures because I feel sometimes posters take advice and do not show the end result of their work to help researchers. I made the changes to the location of the expansion tank, cleaned up the left side, and replaced the lower boiler drain, installed a service valve on the expansion tank, and strapped the 1/2" line to the larger lines above. I welcome all critiques and suggestions for improvement. On the other topics I had, I'll save repiping to receive the Radon Midigation pipe when the boiler is not needed. I also plan on looking in to LWCO's (suggestions on brand/model would be a good start), installation, and running the system with the fill valve shut, might result in a new post if I hit snags. Credit to everyone on this site who can give advice with a hack like me behind the tools and produce a better product than some of the tradesmen that worked on my system.




#57
Member
Join Date: Mar 2015
Location: USA
Posts: 17
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Boiler Noise
Chacho
Is that Webstone valve a #40612 ?
You have got to make sure that the valve is actually draining the tank when the handle is rotated. Is it possible that you are draining the boiler feed and not the tank? If that is the case you need to turn the valve over.
Is that Webstone valve a #40612 ?
You have got to make sure that the valve is actually draining the tank when the handle is rotated. Is it possible that you are draining the boiler feed and not the tank? If that is the case you need to turn the valve over.
#59
Member
Join Date: Mar 2015
Location: USA
Posts: 17
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Boiler Noise
NJT
Perhaps your correct. I use these valves all the time. I have never thought of that. I always looked into them and oriented it by where I want the flow to go before installing them.
I was looking at the arrow diagram on the handle. That diagram on Chacho['s valve is different than what the catalog shows. I think that the valve handle only operates in a counter-clockwise 1/4 turn. The side port should be facing the valve body and not the hose bibb ball valve, except when draining the tank.
Chacho can test it easy enough.
Perhaps your correct. I use these valves all the time. I have never thought of that. I always looked into them and oriented it by where I want the flow to go before installing them.
I was looking at the arrow diagram on the handle. That diagram on Chacho['s valve is different than what the catalog shows. I think that the valve handle only operates in a counter-clockwise 1/4 turn. The side port should be facing the valve body and not the hose bibb ball valve, except when draining the tank.
Chacho can test it easy enough.
#60
Member
Join Date: Mar 2015
Location: USA
Posts: 17
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Boiler Noise
Chacho
We've never paid much attention to LWCOs unless the boiler was above radiation, but now it's code. It should be mounted above the boiler. I like the Mcdonnell & Miller RB-24E, Electronic, 24V Low Water Cut-Off You have a vent damper, but I'm not sure of the voltage. The LWCO wires into the low voltage safety circuit and a 24 volt supply voltage. The probe is self cleaning and must be in the flow stream.
I use a 1" copper tee and a 1" X 3/4" FPT flush bushing, but I make my own. That keeps the probe as far into the flow stream as possible. Use Teflon tape instead of pipe dope on the threads as they are plastic.
This is a true capacitance LWCO. I saw installations using a pressure relay. If the pressure fall below 5-8 psi the circuit opens, shutting down the boiler. But it isn't code and won't pass inspection.
We've never paid much attention to LWCOs unless the boiler was above radiation, but now it's code. It should be mounted above the boiler. I like the Mcdonnell & Miller RB-24E, Electronic, 24V Low Water Cut-Off You have a vent damper, but I'm not sure of the voltage. The LWCO wires into the low voltage safety circuit and a 24 volt supply voltage. The probe is self cleaning and must be in the flow stream.
I use a 1" copper tee and a 1" X 3/4" FPT flush bushing, but I make my own. That keeps the probe as far into the flow stream as possible. Use Teflon tape instead of pipe dope on the threads as they are plastic.
This is a true capacitance LWCO. I saw installations using a pressure relay. If the pressure fall below 5-8 psi the circuit opens, shutting down the boiler. But it isn't code and won't pass inspection.
#61
Homer, the valves with that " T " on the handle are actually designed so that the handle can be reversed. They even come with an extra 'label' that you stick over the one on the handle if you do reverse them... of course that label is useless because it falls off in a year or so...
One can even grind the stop off the handle if they wish to use the valve in either direction without having to change the handle, which is sometimes useful for initial fill and purge in some applications.
One can even grind the stop off the handle if they wish to use the valve in either direction without having to change the handle, which is sometimes useful for initial fill and purge in some applications.
#62
Homer, the valves with that " T " on the handle are actually designed so that the handle can be reversed. They even come with an extra 'label' that you stick over the one on the handle if you do reverse them... of course that label is useless because it falls off in a year or so...
Thanks for the info on the LWCO's. Again, probably a warm weather project for me when I have more time. I may be looking for a lot more detail then, but this will get me started.