Boiler not igniting for 1 Zone on Crown Boiler w. Taco Zone box


  #1  
Old 09-18-14, 01:29 PM
A
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Boiler not igniting for 1 Zone on Crown Boiler w. Taco Zone box

Hello, I have a 3-zoned natural gas boiler(with baseboard heat) . the zones are wired into a Taco brand relay box.

For zone 1, when I set the Tstat above the current temperature, it sends the signal to the Taco relay. (I see the zone 1 light up) but It does not fire the boiler. The thermocoupler is an electronic light-on-demand.
zones 2 and 3 seem to come on but then shut off a few minutes later. I will attach some picks when i get home but any intial suggestions?
Thank you

Anthony
 
  #2  
Old 09-18-14, 02:39 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 19,710
Upvotes: 0
Received 8 Upvotes on 6 Posts
Tell us make/model of the zone valves.

Boiler model and if there is any other 'series' or 'revision' numbers might be helpful also.

Waiting for pics...
 
  #3  
Old 09-23-14, 08:18 AM
A
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Hello,
My appologies for the late reply but wanted to give you an update on this.

So i got home and went to take some pictues..and realized that the PSI was @ 0. I checked into that as the reason and figured out i neede dto put water in the pipes. My concern was it would not keep the pressure (maybe a pipe had burst)..but i filled it up to 12 and it has been fine since.

I hope this helps at least 1 person that might overlook this as a reason.
 
 