TACO outdoor reset when using a priority DHW zone
#1
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 1
Upvotes: 0
Received 0 Upvotes
on
0 Posts
TACO outdoor reset when using a priority DHW zone
I have a ZVC404-EXP zone control set up with a priority zone for DHW (zone valve, not circulator). I also have a PC700 outside reset. It seemed to get stuck in hot water mode because the PC700 set the boiler too close to the DHW setpoint. I am guessing I should switch to a PC702 that will set the boiler to 180 when in priority mode. Is this correct or is there another option? What do I do with the stage 1 and stage 2 outputs of the PC702? Can the DHW demand wires just be paralleled with the zone valve motor for the priority zone?
#2
Hello and welcome to the forums..
For reference...PC 700
http://s3.supplyhouse.com/manuals/13..._PROD_FILE.pdf
Can you tell us the make and model of the boiler please? Also make and model indirect?
Once we get that info we can work on getting an answer to your issue.
For reference...PC 700
http://s3.supplyhouse.com/manuals/13..._PROD_FILE.pdf
Can you tell us the make and model of the boiler please? Also make and model indirect?
Once we get that info we can work on getting an answer to your issue.
#4
It seemed to get stuck in hot water mode because the PC700 set the boiler too close to the DHW setpoint.
You mean that the boiler is operating at the ODR setpoint even on a call from the DHW and doesn't get hot enough to bring the DHW tank up to temperature?
It shouldn't do that. It should fire to high limit on a call from DHW.
Do you have the dipswitch "RESET - NORMAL" pushed over to RESET?