Aquastat help on steam system
#1
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Aquastat help on steam system
Recently purchased a home that has a Burnham IN7 steam boiler. The basement is heated with hotwater from the steam boiler which is circulated with a Bell and Gossett pump controlled by a Honeywell R845A and a separate thermostat in basement. There's a Honeywell L4006A aquastat attached on the hotwater copper pipe but the aquastat isn't connected electrically to anything.
I think the aquastat is supposed to be connected somewhere to limit the temperature of the pumped hotwater to 180 degrees and also to be able to start the boiler if the upstairs thermostat isn't calling for heat?
Does anyone know how this aquastat must be connected?
The boiler has an intermittent electronic pilot connected to a probe type LWCO and a vent damper.
Thanks
I think the aquastat is supposed to be connected somewhere to limit the temperature of the pumped hotwater to 180 degrees and also to be able to start the boiler if the upstairs thermostat isn't calling for heat?
Does anyone know how this aquastat must be connected?
The boiler has an intermittent electronic pilot connected to a probe type LWCO and a vent damper.
Thanks
#2
Member
Join Date: Jul 2009
Location: Toronto
Posts: 1,043
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Post pics please.
How is the B&G controlled now ?
I would think that the aquastat might be installed to prevent steam from hitting the circ if the water level in the boiler dropped.
I do not think you want to fire that boiler on just a basement call for heat, you will over heat the primary boiler load unless it's zoned. If's it is zoned you might be bouncing off the limit (water or steam pressure) a bunch and that short cycling is hard on the boiler and fuel. Steam is already very hard on fuel.
How is the B&G controlled now ?
I would think that the aquastat might be installed to prevent steam from hitting the circ if the water level in the boiler dropped.
I do not think you want to fire that boiler on just a basement call for heat, you will over heat the primary boiler load unless it's zoned. If's it is zoned you might be bouncing off the limit (water or steam pressure) a bunch and that short cycling is hard on the boiler and fuel. Steam is already very hard on fuel.
#3
I would think that the aquastat might be installed to prevent steam from hitting the circ if the water level in the boiler dropped.
B&G used to have an excellent paper on setting up a hot water zone off a steam boiler but since Xylem took over the papers are almost impossible to find. I'll look...
#4
Start here with Dan Holohan:
Hybrid Hydronics, by Dan Holohan - Old-House Journal
Here's the TEXT ONLY of the B&G article... and of course in their infinite wisdom the new proprietors apparently chose not to include the drawings.
http://websupport.completewatersyste...a-Steam-Boiler
Here's the drawing that I believe originally was with that article:
Here's the link to that page with more Q & A from Dan the Man.
https://heatinghelp.com/systems-help...-steam-boiler/
More DtM:
The Limit To A Hot Water Zone Off A Steam Boiler by Dan Holohan - MasterPlumbers.com PlumbViews
Should give y'all enough to chew on for a while.
Hybrid Hydronics, by Dan Holohan - Old-House Journal
Here's the TEXT ONLY of the B&G article... and of course in their infinite wisdom the new proprietors apparently chose not to include the drawings.
http://websupport.completewatersyste...a-Steam-Boiler
Here's the drawing that I believe originally was with that article:
Here's the link to that page with more Q & A from Dan the Man.
https://heatinghelp.com/systems-help...-steam-boiler/
More DtM:
The Limit To A Hot Water Zone Off A Steam Boiler by Dan Holohan - MasterPlumbers.com PlumbViews
Should give y'all enough to chew on for a while.
#5
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
NJ Trooper:
Read the articles by Dan the Man. Thanks
Think I've figured out how to proceed. Let me know what you think.
The boiler and pump comes on at the same time when the basement thermostat calls for heat and the aquastat limits the water to 180 degrees so steam isn't made. Upstairs gets no heat at this point.
If upstairs thermostat is calling for heat the water temp will be about 212 degrees at least, and if downstairs thermostat calls for heat at this point then the aquastat has no effect on boiler but the bypass piping reduces basement watertemp to around 180 degrees.
I've included a schematic.
Read the articles by Dan the Man. Thanks
Think I've figured out how to proceed. Let me know what you think.
The boiler and pump comes on at the same time when the basement thermostat calls for heat and the aquastat limits the water to 180 degrees so steam isn't made. Upstairs gets no heat at this point.
If upstairs thermostat is calling for heat the water temp will be about 212 degrees at least, and if downstairs thermostat calls for heat at this point then the aquastat has no effect on boiler but the bypass piping reduces basement watertemp to around 180 degrees.
I've included a schematic.
#6
Yes, I believe that's all correct.
Is the system piped as shown with the bypass and all? Bronze pump?
If so, then you should be good to go.
If all of your baseboard in the basement is below the water line of the boiler, the flow check valves may not be necessary.
Many hot water loops off steam boiler don't include the bypass... probably installed by the uninformed... they really should have that.
Is the system piped as shown with the bypass and all? Bronze pump?
If so, then you should be good to go.
If all of your baseboard in the basement is below the water line of the boiler, the flow check valves may not be necessary.
Many hot water loops off steam boiler don't include the bypass... probably installed by the uninformed... they really should have that.
#7
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Unfortunately there's no bypass so I'm going to add that before I proceed with the re-wiring. Pump isn't bronze, it's the red pump. I'll leave that until it dies. Incidentally the pump flow is in the wrong direction. It's pumping into the boiler via the equalizer instead of pumping into the baseboard radiation. I checked the Bell and Gossett site and found how to flip the direction of pump flow. It seems that the only correct thing done on this install was having the pipes and baseboards below the boiler water line. Later in the week I'll attempt to remedy the situation.
Thanks for your help NJ Trooper
Thanks for your help NJ Trooper
#8
Pump isn't bronze, it's the red pump
It seems that the only correct thing done on this install was having the pipes and baseboards below the boiler water line
Let us know how it goes!