Ferroli Domina F24E boiler, stops (block) after couple of seconds...
Old 10-22-14, 09:40 AM
I
Hi everyone and thanks for any input in advance.
I have a Ferroli Domina F24E boiler that stops (block) after couple of seconds...
I didn't open the combustion chamber because I don't know whether it is safe or not but from its cover's small window I can see a blue flame before the block.
In the manual there is written to check the following:
1) gas input
I have seen the flame so I guess it is OK
2) air in the pipes
I let air out of the radiators and reset pressure between 1 ,5 and 2
3) electrodes
I would like to check them but do you think I can safely turn the boiler on with the combustion chamber open?
Old 10-22-14, 10:14 AM
NJT's Avatar
NJT
NJT is offline
Received 8 Upvotes on 6 Posts
You are asking about a boiler that I don't believe is sold in the USA. So I wonder why your profile indicates that your location is in IOWA , US ?
The majority of ppl that visit this website are US based and probably do not have experience with European made heating products.
Old 10-22-14, 10:25 AM
Grady's Avatar
Received 40 Upvotes on 38 Posts
One of the most common problems with any gas fired heating appliance with the symptom you describe is a dirty flame sensor. These sensors are usually a rod which is enveloped by the flame. Often removal & cleaning with a Scotch Brite pad will cure the problem.
Old 10-22-14, 12:08 PM
I
Doh, didnt realize those were US states. I was actually looking for IT but it was not there.
Thanks for the tip Grady. I think what you describe there is what the manual calls electrod.
I will open all the windows and the combustion chamber & hope for the best.
Sorry for the non US intrusion.
Old 10-22-14, 12:37 PM
Grady's Avatar
I looked at some parts diagrams & it appears there are two rods. The one with a simple 90* bend would appear to be the flame sensing rod.
Old 10-22-14, 01:03 PM
NJT's Avatar
NJT
NJT is offline
No apology needed! I just wanted you to know that we might not know your equipment. We're happy to help anyone if we are able...
And Grady is able! (as usual!)
Old 10-22-14, 04:54 PM
Grady's Avatar
Thanks Troop. I'm not sure about which electrode is which cause my German(?) don't be so real goot.
Old 10-22-14, 07:28 PM
NJT's Avatar
NJT
NJT is offline
Nein, es ist nicht Deutsch, è Italiano.
Είσαι ακόμα ο καλύτερος!
If that sounds like Greek to you, it's because it is!
The manual is in English! Hooray!
https://www.heatingspares247.com/dow...cal_Manual.pdf
I believe it's item #82 on page 8.