Boiler zonevalve and thermostat
#41
Looks like I had it bassackwards, story of my life:
Flo-Control Valves are vertical lift check valves that function when the system pump starts. Flo-Control Valves are designed with a handle that when turned fully counterclockwise will permit gravity circulation. This is useful in emergency situations whenever electrical power is lost and only partial heating is possible.
During system filling and purging it may be helpful to Manually open the Flo-Control Valve to aid in air removal. Do, this by turning the handle counterclockwise to the fully open position.
During system filling and purging it may be helpful to Manually open the Flo-Control Valve to aid in air removal. Do, this by turning the handle counterclockwise to the fully open position.
IMPORTANT: If handle is left in the manual open position, uncontrolled heating of room radiation will occur. If after power outage or system air venting the manual flow feature was used, make sure the Flo-Control is returned to automatic operation.
#42
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
#43
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I followed the old thermostat wires from the boiler to the basement ceiling and I see that they are wirenutted together with a different wire. This wire then goes off to the t'stat.
The pattern seems consistent, I can turn up the t'stat causing the burner to start, and turn down the t'stat causing the burner to stop. However, if I leave the t'stat after it kicks off the burner it does not turn off the burner even if the temperature increases above what the t'stat is set at. The burner only stops when it reaches the high limit. Also, it appears that the circulator pump keeps going and going.
Could this have something to do with the red and white wire being connected to the wrong terminals. What will happen, worst case, if I swap the red and white wire?
The pattern seems consistent, I can turn up the t'stat causing the burner to start, and turn down the t'stat causing the burner to stop. However, if I leave the t'stat after it kicks off the burner it does not turn off the burner even if the temperature increases above what the t'stat is set at. The burner only stops when it reaches the high limit. Also, it appears that the circulator pump keeps going and going.
Could this have something to do with the red and white wire being connected to the wrong terminals. What will happen, worst case, if I swap the red and white wire?
#44
Could this have something to do with the red and white wire being connected to the wrong terminals. What will happen, worst case, if I swap the red and white wire?
Are they the type with the mercury vial inside? (please dispose of responsibly! Mercury does not belong in a landfill!)
It sounds as if you won't need much justification for those new thermostats now!
#45
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yeah I agree. Perhaps it is time for new thermostats. These are the ones with the mercury vial inside.
I did do the same measurements as I did on the old RA89, on that one I only had 14VAC across the terminals on the SR502-4 I have 28VAC across all terminals except for when it is active then it is 0VAC.
The described behavior is for both zones. I believe the wiring is correct. I have power coming in to a dedicated switch. From there I power the a'stat and the new SR502-4 panel. Both of the pumps are hooked up to the SR502 and each thermostat is connected to the respective zone and the endswitch is connected to TT on the a'stat
I did do the same measurements as I did on the old RA89, on that one I only had 14VAC across the terminals on the SR502-4 I have 28VAC across all terminals except for when it is active then it is 0VAC.
The described behavior is for both zones. I believe the wiring is correct. I have power coming in to a dedicated switch. From there I power the a'stat and the new SR502-4 panel. Both of the pumps are hooked up to the SR502 and each thermostat is connected to the respective zone and the endswitch is connected to TT on the a'stat
#46
The described behavior is for both zones
I thought only one of them...
This changes my thinking a little bit, but I'm not sure what it means exactly.
I believe those thermostats have an 'anticipator' dial inside, don't they?
It should be labeled as 'shorter' <---> 'longer'.
Where is it set?
I have 28VAC across all terminals except for when it is active then it is 0VAC
#47
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yes both of them.
It did have an 'anticipator' dial. Here is a picture
https://drive.google.com/file/d/0B_T...ew?usp=sharing
It did have an 'anticipator' dial. Here is a picture
https://drive.google.com/file/d/0B_T...ew?usp=sharing
#49
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It turned off after running for a couple of minutes. wahoo. It is still hot as hell but perhaps if I let it cool down overnight, I can do some fresh tests tomorrow. I must have turned it down past .15, I am not exactly sure, but it turned off. The temperature is still a bit higher than the t'stat but this I hopefully can fine tune.
#51
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Nope no level. They've been hanging on the wall as long as I can remember. No knowing if the installer had them level from the beginning but they have not moved as far as I know, always been in the same spot
#52
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I pushed the anticipator dial all the way down on both t'stats, and things have improved significantly. The heat call comes in and the burner starts, and the t'stat shuts it down when the temperature is reached. The burner also stops before hitting the max temperature setting of the a'stat. After our conversation on the a'stat, and the fact that I moved the circulator to the Taco SR, I put the red and white wire back and just pulled the blue wire and put a wirenut on.
It's interesting to me that changing the relay from the old RA89 and moving the circulator off the a'stat, had me making such a significant (I think) change to the t'stats.
As far as cutting the pipes, were you able to see the new photos I uploaded in post 42? I was not able to edit my old post 29.
It's interesting to me that changing the relay from the old RA89 and moving the circulator off the a'stat, had me making such a significant (I think) change to the t'stats.
As far as cutting the pipes, were you able to see the new photos I uploaded in post 42? I was not able to edit my old post 29.
#53
It's interesting to me that changing the relay from the old RA89 and moving the circulator off the a'stat, had me making such a significant (I think) change to the t'stats.
As far as cutting the pipes, were you able to see the new photos I uploaded in post 42? I was not able to edit my old post 29.