flame detection electrode with a multimeter?
Old 11-03-14, 11:39 AM
I
Hello there,
I was wondering if there is any way to check the state (new, old, about to fail) of a flame detection electrode with a multimeter?
Old 11-03-14, 01:09 PM
lawrosa's Avatar
Super Moderator
Received 79 Upvotes on 71 Posts
Im sure there is... Probably resistance in ohms..
Can you tell us what product the flame sensor is used in???
Old 11-03-14, 04:34 PM
Received 3,485 Upvotes on 3,128 Posts
The actual rod plays no part in flame sensing. Let me explain.... it's just a piece of metal that sits in the flame and is a conductive part of the circuit. The only thing that can go wrong with a flame sensor rod is that it becomes coated with gas byproducts which cause the rod to be insulated.
To measure the effectiveness of a flame rod.... you disconnect the wire from the rod and you put a meter in line set to DC microamps and you read the scale. The rod conducts thru the flame to ground.
If you suspect a flame rod sensor issue..... usually you just need to clean it good with a scotchbrite pad or very fine emery cloth. You want the rod to be very shiny and clean.