Bleeding slantfin hydronic
When bleeding the slantfin hydronic radiator lines should the circulator be on or off?
I am thinking on so it pushes air bubbles toward the bleeder valve.
Thanks
Thanks
Originally Posted by zoneout
". . .I am thinking on so it pushes air bubbles toward the bleeder valve . . ."
Otherwise, you get more water than air.
To bleed radiation of air increase the boiler water pressure to 25 psi. have flow only to the zone to be bleed , the pressure will make the air bubble smaller and the flow will move the bubble to the air vent.
You'll get as many opinions one way as you will the other.
Fact is that the only 'correct' way is the way that works.
There's valid reasons for bleeding cold, hot, pump running, not running...
Maybe the questions from us to you should be
" What is the problem? " " Why do you want to bleed your system? "
The problem is there are 3 floors each a separate zone with its own circulator. 1960s original slantfin baseboard with American standard boiler. Anyway yesterday I noticed the top floor circulator was running constantly. So I touched the return pipe and it was cool. All I can figure is that there is a lot of air in the line blocking the flow.
there are 3 floors
If you try to bleed the 3rd floor rads and nothing comes out, or air acutally gets sucked INTO the bleeder, it means there isn't enough pressure in the system.
Go to the boiler and tell us the readings on the PRESSURE / TEMPERATURE gauge.
Pressure 15 psi and temp fluctuating between 130 to 170.
Btw, the lower 2 floors seem fine.... Return pipes quite warm to the touch.
First off, chances of a boiler gauge being accurate are slim. Those old square gauges were pretty good though. But read this:
http://www.doityourself.com/forum/bo...ure-gauge.html
Presuming that the gauge is in fact accurate, your pressure is probably too low.
Lets say your three story home has the highest piping 30' above the boiler.
The MINIMUM pressure when the boiler is cold would need to be SEVENTEEN PSI... and that's COLD. Pressure will be higher when the boiler is heated.
Any less pressure in the system will mean that the upper radiators are below atmospheric pressure and air bubbles will form and the flow will be stopped.
So, before you try to bleed, you need to determine that your pressure gauge is accurate, and find the reason that the pressure in the system is low, and then raise the pressure up to where it needs to be.
and THEN bleed the air out.
I'm guessing that you have the old style expansion tank in the joists above the boiler, correct?
I'm pretty sure once you raise the pressure to get the hot water back to the upstairs you are going to be telling us that now the pressure relief valve is leaking.
Then we're going to have to instruct you how to drain that expansion tank properly...
That's the thing with these old systems... one thing happens and it snowballs into a whole string of things because they are all dependent on each other.
Thanks. Ok - will be putting together a verification gauge tomorrow.
I would estimate the top floor baseboards to be about 20 feet max above the boiler (I counted the basement as 1 story)
Water pressure comes from NYC supply and thru the automatic feeder valve.
Your guess on the old-school expansion tank in the joists is correct!
If that's the case, then 12-15 PSI when the boiler is cold is fine.
If you're seeing 15 PSI when the boiler is at 170F it's still probably a bit low in pressure because when the boiler cools it likely goes below 10 PSI (or less!)
Can you take and post some pics of your system so we can look to see what valves you have available that will facilitate purging the air from the zones?
I do also advise a drain of your expansion tank.
More questions:
Do you produce domestic hot water with your boiler? or is there a separate stand alone water heater?
Do you know if your boiler is a 'warm start' where the boiler maintains a warm temperature at all times regardless of a heat call from the thermostat? Or is it a 'cold start' that would cool completely if there were no heat call?
Right... 2-story home with boiler in basement. Sorry, my bad.
The only valves I know of are the typical screw-type manual bleeders on the baseboards. There are about 3 of them in that top floor zone in different rooms. I didn`t notice any type of bleed valve around the boiler itself.
I did the knuckle-tap test on the expansion tank and it sounded mostly hollow (about 3/4 empty is my guesstimate).
Separate stand-alone water heater. (Though at some time in the distant past there may have been a tankless coil used from the boiler - just a hunch)
Boiler is warm-start with a Honeywell aquastat low limit set at 150 deg and 15 deg differential.
What is the HIGH setting?
OK, sorry for the delay. Got some photos.
Couldn`t see any abandoned pipes from the boiler so looks that HW was always separate tank.
Aquastat high is at 180. There are separate circulator relays through so I dont think the Aquastat high comes into play.
Here are the photos....
![Name: IMG_0746[1].jpg
Size: 36.4 KB](https://www.doityourself.com/forum/attachments/boilers-home-heating-steam-hot-water-systems/43745d1419376786-bleeding-slantfin-hydronic-img_0746-1-.jpg)
![Name: IMG_0747[1].jpg
Size: 40.5 KB](https://www.doityourself.com/forum/attachments/boilers-home-heating-steam-hot-water-systems/43746d1419376856-bleeding-slantfin-hydronic-img_0747-1-.jpg)
Your gauge is showing just a hair over 12 PSI with the boiler at 180F. This is too low even for a 2 story home because it means when the boiler cools the pressure is going to be way below that.
Show me the expansion tank and the piping to it.
Show me the water feed valves.
OK, 55 year old American made boiler gauge still accurate. Verification gauge below shows the same reading of about 12.5 pounds.
![Name: IMG_0762[1].jpg
Size: 21.8 KB](https://www.doityourself.com/forum/attachments/boilers-home-heating-steam-hot-water-systems/44045d1419909654-bleeding-slantfin-hydronic-img_0762-1-.jpg)
Here is the expansion tank with water feed valve to the left...
![Name: IMG_0768[1].jpg
Size: 32.4 KB](https://www.doityourself.com/forum/attachments/boilers-home-heating-steam-hot-water-systems/44046d1419909816-bleeding-slantfin-hydronic-img_0768-1-.jpg)
There is a shutoff valve on the line feeding into the expansion tank just out of view on the photo.
I'm not sure the piping...
I see a water line coming up, a ball valve, then into the pressure reducing valve, out of that valve and doubling back toward the wall where there is another ball valve, then that connects to that vertical pipe?
Is that correct?
Now the expansion tank piping... I see the pipe coming down and toward the wall from the tank, but then it either tees into that other vertical pipe, or it elbows down to someplace... and you say there is a valve below, out of the picture.
Is it the camera angle that makes it look like it's teeing into that vertical pipe? And that vertical pipe is 'hiding' behind the pipe from the tank?
Is that correct?
Right - the black vertical pipe from the ceiling is the cold water supply - the tee in the middle feeds the boiler and the elbow at the bottom goes to the HW tank.
Right - the camera angle makes it look like the expansion tank pipe tees into that pipe in the back. Thats actually the return pipe (foam wrapped) from the HW tank going up into the ceiling.
The pipe from the expansion tank just goes down into the boiler and there is a shutoff valve just out of view.
#21
OK then...
The first thing you should do is drain that tank.
The only 'tricky' part about that is once you start draining, a 'vacuum' will build in the tank and the drain flow will stop. You'll think it's empty, but it's not.
Using the shortest and largest diameter hose possible, with no coils, loops, etc will help.
Close the valve leading to the tank to isolate from the system (of course, shut the boiler down while doing this) and connect hose to drain.
Open drain to start emptying...
when flow stops, you need to break the vacuum.
Sometimes just leaving the hose on the drain a bit loose will be enough to allow it to suck air, or taking it off and putting bucket under and opening drain will allow it to take a 'gulp' of air.
In the olden days guys with better lungs and immune systems than I have would blow into the end of the hose... do that at your own risk... and understand that you could end up with a mouth or face full of nasty old boiler water...
Do you have a small air compressor? If so:
Even if you don't have the compressor, using a wye fitting will make it easier than putting the hose on and taking it off.
After you got the tank empty, and you're sure it's empty, close the drain and open the valve to the tank.
Water will feed and the tank will refill 1/2 to 2/3 with water and you will have an air cushion at the top of the tank.
With boiler now cold, check pressure... it should be right around 15 PSI.
With that out of the way, we can purge the upstairs zone... next...
#22
Ya know what? I just looked at the first tank pic again and it looks like there might be a 'vent' fitting on that drain.
Is that a screw on the side of the fitting above the tank drain valve?
That might make it easier to get air into the tank if it is what I think it is.
Can you get a closer shot of that please?
#23
Yep, that was a vent fitting. When I backed out the screw, water started gushing out. Sure beat blowing into the hose. Thanks, all went smoothly. Pressure right back up to 15 psi.
![Name: IMG_0774[1].jpg
Size: 40.7 KB](https://www.doityourself.com/forum/attachments/boilers-home-heating-steam-hot-water-systems/44092d1420006143-bleeding-slantfin-hydronic-img_0774-1-.jpg)
![Name: IMG_0775[1].jpg
Size: 24.0 KB](https://www.doityourself.com/forum/attachments/boilers-home-heating-steam-hot-water-systems/44093d1420006178-bleeding-slantfin-hydronic-img_0775-1-.jpg)
#24
I'm amazed at those old square gauges... they were quality built! Ahhh, the good old days!
Are you saying that the pressure dropped in the boiler when you were draining the tank?
It should not have, since you had the valve between tank and boiler closed... it might have dropped when you reopened that valve, but would have recovered quickly.
When the boiler fires now, how high does the pressure go when it's HOT?
Still no heat upstairs?
#25
Will go back to get the pressure when hot shortly..... thanks.
#26
#27
OK, so checked today and my system is defying the laws of physics. With the boiler hot the pressure went down to 14 psi.
![Name: IMG_0781[1].jpg
Size: 37.2 KB](https://www.doityourself.com/forum/attachments/boilers-home-heating-steam-hot-water-systems/44183d1420156252-bleeding-slantfin-hydronic-img_0781-1-.jpg)
#28
I happened to notice a real slow drip from the expansion tank feed shutoff valve. About a drop every 3 minutes. Could that cause this problem?
#30
You still haven't answered...
STILL NO HEAT UPSTAIRS?
#31
What now?
If it starts leaking again, and tightening the packing nut doesn't help, try opening the valve all the way onto its backseat, assuming it has one.
#32
#33
The other gauge agrees?
#34
might buy me time until I can replace the darn thing.
What's the clothes pin for?
The return pipe from upstairs is cold.
Turn boiler OFF and allow to cool to 100F or less... you do NOT want to feed a lot of cold water into a HOT boiler! This is important!
CLOSE all three of the yellow handle ball valves.
Connect hose to drain above the ball valve on the zone that's not heating.
Submerge end of hose into a bucket so you can see when bubbles stop.
That lever on top of the pressure reducing valve is your 'fast fill' lever. Lifting that will bypass the regulator portion of the valve and allow a faster flow to push the air out.
Open the hose drain.
Lift the lever on the reducing valve and keep an eye on the pressure gauge. You can 'modulate' that lever and keep the pressure below 30 PSI in the boiler. Keep feeding water at a fast rate until no more bubbles.
Release fast fill lever, close drain.
Open yellow ball valves.
Return to service... should be OK now.
Make sure pressure in boiler when cold is at LEAST 12-15 PSI.
#35
#36
OK, got enough air out of the top floor zone to fill a blimp. Back in service and the return pipe is hot now. Pressure 16 psi cold and 18 hot. I think that slow valve leak allowed the pressure to drop before. Seems steady now but I`ll keep an eye on it.
![Name: IMG_0810[1].jpg
Size: 36.7 KB](https://www.doityourself.com/forum/attachments/boilers-home-heating-steam-hot-water-systems/44365d1420445273-bleeding-slantfin-hydronic-img_0810-1-.jpg)