I have a basic 5ish year old New Yorker natural gas boiler with a Honeywell FocusPRO 6000 thermostat. I'm in Minnesota but the weather has been fairly mild and my thermostat was cycling on every 5 minutes or so. Now that we're finally getting some steady well-below-freezing temps, it still seems to be cycling quite quickly. I'd like to change this so it kicks on every 30 minutes or so, even if it means the temp in my house fluctuates a degree or three. I've gone through the thermostat manual and ensured that all the settings appear correct, so perhaps I'm asking more than my current system can handle. Would I be wise to replace the thermostat? It seems like it might pay for itself in the long run on efficiency and prolonging the life of the boiler.
Here's the install manual for my current thermostat.
https://customer.honeywell.com/resou...69-2738EFS.pdf
Aquastat is a L 4080 B 1436. Some Googling suggests to that the range is 140-240.
My house is about 1300 square feet and the boiler apparently has an output of 45000 BTU. I figure that I have decent though not great insulation and windows. From what I can tell the boiler is more or less properly sized for my house, though I'm just trusting a few calculators that are out there on that.
Is there any other info I can provide? Does this even make sense? Essentially, my understanding is that the less frequent a boiler cycles the more efficient it will be and the greater longevity it will have. I'm striving for that goal even if it means sacrificing temperature consistency a bit. Thanks in advance.
Old 01-04-15, 07:29 PM
lawrosa's Avatar
Super Moderator
Received 60 Votes on 52 Posts
Make and model of boiler will help..
Also for reference tell us the psi and temp reading off boiler gauge.
Please also tell us what type of heat emitters you have in the home... cast iron? copper finned? etc...
Pic of the boilers piping and boiler itself would be great...
And last how is your hot water heated?
The T stat may not be the issue..
Old 01-04-15, 07:39 PM
NJT's Avatar
NJT
NJT is offline
Received 3 Votes on 2 Posts
Is the thermostat located on an interior wall?
Is the thermostat located away from the direct effect of a nearby heat emitter (baseboard/radiator)?
Where the thermostat wire exits the wall, is the hole around the wire sealed? Or is it possible that a cool draft is coming out the hole and causing the thermostat to short cycle?
To what do you have "FUNCTION 5" set to?
What temperature setting do you have the L4080 at?
Old 01-04-15, 07:49 PM
NJT's Avatar
NJT
NJT is offline
You're sure that the thermostat is what's cycling, right?
You observe it on the display?
Old 01-05-15, 06:44 AM
P
It's a New Yorker CG30CNC-TE2. I've got the pressure at about 12-15 (cold-hot). I've got seven cast iron radiators that I'd call medium (on average) in size. Hot water is heated via its own power.
The thermostat is located on an interior wall in a hallway, though it's only ~10 feet from the (small-ish) bathroom radiator. Hole behind the wall is small, though I can shoot some expanding foam into hole for the thermostat wire in the basement if you think that might help. There's certainly no reason truly cold air should be rushing in and out of that hole. Function 5 is set to 5: gas or oil furnace.
I'll try to get more detailed info this evening, including looking at the aquastat and paying closer attention to the display of the thermostat when this cycling takes place. I believe the thermostat is involved, as I hear the click that it makes when this occurs.
Old 01-05-15, 06:52 AM
NJT's Avatar
NJT
NJT is offline
No... one would think not, but it can effect thermostat operation, even if it's only a few degrees cooler than the room.
Is the thermostat new? I wonder if it could simply be defective?
Old 01-05-15, 07:00 AM
NJT's Avatar
NJT
NJT is offline
This is the 'cycles per hour' setting.
As experiment, try reducing that number and note the results.
Old 01-05-15, 07:12 AM
P
The thermostat is new. It was installed by a contractor when I had a high velocity AC unit installed. I'll try sealing up the wall and playing with that cycles per hour setting to see if I can get more favorable behavior. I'll also see what I can find with the aquastat regarding settings and the real temp range that the boiler is showing as it cycles.
Old 01-05-15, 07:09 PM
P
I verified that when the system shuts off it's the thermostat that initiates the change ("Heat On" disappears on screen). The aquastat appears to be showing ~155 degrees, but the gauge on the boiler appears to top off at roughly 130 degrees and 14psi.