Single zone baseboard heat (cast iron) but one floor is not getting hot..

Hello all.
I have a split level home with 4 floors.
The top 2 floor baseboard get really hot but the bottom level does not.
The boiler is in the basement which is finished but it is hot for the heat thrown off the boiler. Yesterday I did some research one end of the baseboard has a nozzle so I screwed a hose on it and let out a lot of water and it got hot on that side of the cast iron baseboard but not the other. There was a bleed valve on the other end so I bled it until the water was hot and then the whole baseboard got really hot but did not stay hot. There is a valve under the bleeder that I turned but did not hear water going through so I think it may be broken.. Anything else I can try before I call someone to replace the valve.. This room that the baseboard is in is against the wall next to the garage so it was freezing on that level the last couple day here in nj..
 
Sponsored Links
  #2  
Old 01-18-15, 04:58 PM
S
Member
Thread Starter
Join Date: Jan 2015
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
Anyone?

Anyone have any idea what I can try or know anyone in north Nj that is reputable and can help?
 
  #3  
Old 01-18-15, 05:13 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
Hi Stoned,

Sorry we seem to have missed your first post... happenz time to time.

Do you happen to know if your system is piped with what are called 'Monoflo(tm)' tee fittings?

These can be difficult to bleed air from...

I was going to say that you might possibly have a freeze up, but you said you were able to get the whole baseboard hot by bleeding it, so maybe not.

Can you take and post some pictures of your boiler system?

Also, look for where the pipes to the baseboard come off the main pipe and look carefully at those tee fittings. If there is an ARROW indicating flow, or possible a red ring, you may have monoflo...

Take a picture of the tee fittings too.

I'm sorry that rulz don't allow us to provide references ... not Angie's List...
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: