Indirect DHW tank always on with zone valve installation?

I was looking thru installation instructions for superstore contender indirect water heater and I came across this diagram for installation with zone valves:

Name:  DHW.jpg
Views: 4549
Size:  45.4 KB

I don't see a zone valve on the DHW zone so it seems that hot water will flow thru the tank when DHW calls for heat or when any other heating zones call for heat.

if DHW has priority the other zones will be shut off, but it seems that DHW will always be on with or without a call for it.

is this typical installation? i wonder if it's a mistake since there is another oddity on the diagram - there are 3 outgoing pipes for 3 zones and there are 4 intake pipes. I wonder if one of those intakes with a zone valve supposed to be to the DHW tank.
 
Sponsored Links
  #2  
Old 01-21-15, 02:40 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
I don't grok that diagram at all. Looks like a mistake to me too...

Whoever drew that probably went on coffee break and then forgot where he left off cutting and pasting from the other diagram.

What's with the pump?

If using zone valves, definitely go with the 1" that the diagram calls for.

If using pumps, you need flow check valves so the heating zones can't pump through the WH, and vice versa.
 
  #3  
Old 01-21-15, 02:43 PM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
Figure 5 in this one is better, but the pump location is still whack:

http://www.htproducts.com/literature/lp-65.pdf

I wonder how these ever get installed correctly?

(not that installers ever read the instructions... maybe this time it's a good thing?)
 
  #4  
Old 01-21-15, 02:50 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,145
Received 60 Votes on 52 Posts
The drawings are piss poor... I would ignore them..

Figure 6 -
Installation with Circulators is a little better... just pretend your using zones on the system side .

A call to their engineers is in order IMO...

http://www.htproducts.com/literature/lp-65.pdf
 

Last edited by lawrosa; 01-21-15 at 02:52 PM. Reason: Sry... posted same time as Trooper...
  #5  
Old 01-22-15, 05:36 AM
_
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 332
Received 0 Votes on 0 Posts
ok, thank you guys. i thought i was going crazy

and it looks indeed that 4th line was supposed to be the line going to indirect. and the pump is in the wrong place too
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: