No circulator this morning


  #1  
Old 01-28-15, 05:43 AM
T
Member
Thread Starter
Join Date: Jun 2012
Posts: 1,060
Received 31 Votes on 25 Posts
No circulator this morning

Honeywell 8124 with L1 jumped to ZC to run circ whenever there's a call for heat. That was done because of the actions of an HW+.
This morning I have no circulator, nothing between C1 & C2. L1 to ground gives me 110. The baseboards are warm, I imagain from gravity flow, the house is losing temp slowly. Aquastat issue?
 
  #2  
Old 01-28-15, 07:29 AM
T
Member
Thread Starter
Join Date: Jun 2012
Posts: 1,060
Received 31 Votes on 25 Posts
Update: Failed solder joint, heating up the iron now.

Update #2: Joint fixed, wired up and I'm running once again.

If it weren't for the great info on this site, that would have been a costly repair!
 

Last edited by tomf63; 01-28-15 at 09:04 AM.
 