Priority DHW

I currently have the switch for my indirect DHW zone of the Taco box set to priority. Are there any opinions out there as to keeping it like this, or taking the priority off?

Reason I ask is because I notice sometimes, when there is DHW demand as well as heat demand, when the DHW is satisfied, the boiler will shut down, but then kick back on right off to deal with the heat demand.
 
Sponsored Links
  #2  
Old 01-30-15, 10:32 AM
NJT's Avatar
NJT
NJT is offline
Member
Join Date: Oct 2006
Location: USA
Posts: 23,539
Received 3 Votes on 2 Posts
You really only need the priority on if the boiler is too small to handle reheating the DHW tank AND providing heat for a space heating call. If your tank seems to recover in an adequate amount of time even when there is a simultaneous heat call, then you can switch priority off.
 
  #3  
Old 01-30-15, 11:08 AM
N
Member
Thread Starter
Join Date: Dec 2014
Posts: 207
Received 0 Votes on 0 Posts
Thanks NJ, that's what I suspected, just wasn't 100% sure. Maybe I will try it out and see how it goes.
 