I have a problem that hopefully one of the experts in this forum can help me with. I live in a ranch house that has baseboard heating through a gas boiler which feeds 3 zones (basement, bedrooms, and living/dining room).
I've noticed the past few days that when the thermostat is turned "OFF" in the dining/living room but "ON" in the bedroom, the baseboards are giving off heat in the dining/living room as well as the bedrooms. Ive tested the thermostat "ON/OFF" switch that feeds the dining/living room zone and it seems to function properly (the solenoid on the control box on the boiler opens and closes like it is supposed to). When I turn the thermostat that controls the bedroom zones to "OFF" then ALL of the heat is shut off in the entire house (the basement zone is unaffected by either of the other two zones being turned on or off, and the basement zone functions properly).
I always thought the zones were completely independent of each other and didnt share any of the same pipes? So I'm confused how the dining/living room is being controlled by the bedroom zone?
Any advice/help would be greatly appreciated
I've noticed the past few days that when the thermostat is turned "OFF" in the dining/living room but "ON" in the bedroom, the baseboards are giving off heat in the dining/living room as well as the bedrooms. Ive tested the thermostat "ON/OFF" switch that feeds the dining/living room zone and it seems to function properly (the solenoid on the control box on the boiler opens and closes like it is supposed to). When I turn the thermostat that controls the bedroom zones to "OFF" then ALL of the heat is shut off in the entire house (the basement zone is unaffected by either of the other two zones being turned on or off, and the basement zone functions properly).
I always thought the zones were completely independent of each other and didnt share any of the same pipes? So I'm confused how the dining/living room is being controlled by the bedroom zone?
Any advice/help would be greatly appreciated

#3
Member
Thread Starter
Join Date: Jan 2015
Location: USA
Posts: 10
Likes: 0
Received 0 Likes
on
0 Posts
Spott,
Thanks for the quick reply! I have one circulating pump and 3 zone relief valves (I've attached some pictures for reference). I have not had the system worked on lately, and it only started happening about 2 days ago. Before that everything functioned normally.
Thanks for the quick reply! I have one circulating pump and 3 zone relief valves (I've attached some pictures for reference). I have not had the system worked on lately, and it only started happening about 2 days ago. Before that everything functioned normally.

#5
I can see two zone valves in your pictures. You'll need to check each one to see if it's closing and operating correctly with its own thermostat.
#7
Member
Join Date: Dec 2013
Location: USA
Posts: 228
Likes: 0
Received 0 Likes
on
0 Posts
Your zone valves are (from Left to Right) Dinning room, Bed room, Basement.
On top of each valve is a manual opening lever, verify that there is room above the Living room valves manual open lever and the electrical box, should be room for a finger.
To test place all valve levers in AUTO
Turn off all thermostats.
Verify boiler stops firing.
1) For each thermostat in turn, turn up one thermostat verify that pump starts and boiler fires (boiler cool)
2) Turn down thermostat and repeat 1) with next.
On top of each valve is a manual opening lever, verify that there is room above the Living room valves manual open lever and the electrical box, should be room for a finger.
To test place all valve levers in AUTO
Turn off all thermostats.
Verify boiler stops firing.
1) For each thermostat in turn, turn up one thermostat verify that pump starts and boiler fires (boiler cool)
2) Turn down thermostat and repeat 1) with next.
#8
Sometimes, even if the valves appear to respond to the thermostat properly they can get stuck open.
When the valve is OPEN the auto/manual lever will move with no effort, Lucy Goosey.
When the valve is CLOSED moving the lever takes a little effort, and you will hear the 'whirring' of the gears inside as you move the lever.
When the valve is OPEN the auto/manual lever will move with no effort, Lucy Goosey.
When the valve is CLOSED moving the lever takes a little effort, and you will hear the 'whirring' of the gears inside as you move the lever.
#10
Member
Thread Starter
Join Date: Jan 2015
Location: USA
Posts: 10
Likes: 0
Received 0 Likes
on
0 Posts
Fellas - I think your suggestions did the trick! The valve for the dining/living room opened and closed and is now functioning as it should. Hopefully it won't happen again, but if it does I know where to begin my troubleshooting. Thanks again for your help!