Bleeding Boiler Zones Help

I have a gas boiler with 2 zones, 2 circulator pumps and 2 relays. See attached diagram

When I bleed the system this is what I basically do. I turn all the shut-off valves off, except for line going out to the baseboards of the zone I am going to bleed, disengage the fill valve pressure regulator and then I open the drain petcock above the circulator pump and let it run for about a minute or two and then repeat for the second zone. However, when I do the above the tridicator gauge shows 0 psi pressure.

Is the way I am bleeding the system correct?Name:  Heating System Model (1).jpg
Views: 467
Size:  19.5 KB
 
Sponsored Links
  #2  
Old 12-02-15, 05:45 AM
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 1,126
Upvotes: 0
Received 21 Votes on 18 Posts
Your procedure for venting the zones is OK. Your diagram does not show the location of the pressure gage and the fill valve. If you can get 15-20 psi on the pressure gage using the fill valve after you shut off the zone drain valve, you are OK. I would not be concerned with the gage reading 0 when either drain valve is open.
 
  #3  
Old 12-02-15, 06:40 AM
Member
Thread Starter
Join Date: Nov 2015
Posts: 7
Upvotes: 0
Received 0 Votes on 0 Posts
The pressure gauge is mounted behind the boiler cover. The fill valve is goes into zone 1 and branches into zone 2.

I am thinking my fill valve is malfunctioning (B&G FB-38), because when I open the drain above the circulator pump all the way, there is only a trickle of water coming out of the hose once the pressure drops to 0 psi. Hence, the fill valve is not doing its job.
 
  #4  
Old 12-02-15, 07:38 AM
Member
Join Date: May 2006
Location: upstate New York
Posts: 397
Received 0 Votes on 0 Posts
pressure

That fill valve, I think, has a "handle" that can be lifted to bypass the pressure reducing part of the valve and flow a larger amount of water. That might be worth a try. Might not work if the screen in the valve is clogged up. Good luck-
Steve
 
  #5  
Old 12-02-15, 08:48 AM
Member
Thread Starter
Join Date: Nov 2015
Posts: 7
Upvotes: 0
Received 0 Votes on 0 Posts
I spoke to Bell and Gossett technical support and they said the same thing Steve said, to check the strainer on the fill valve to make sure it is not clogged. They infromed me that these fill valves rarely if ever fail.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: