Adding common wire to two-wire system

Hi guys -- I have a fairly new boiler with a GeniSys 7505 burner controller connected directly to a Nest thermostat. The controller has only two wire terminals. This is causing problems with the nest, which "pulses" the wire to steal power. So what I want to do is add a C wire. What's the best way to do this? I already have extra wires running from the thermostat, but can use more if necessary. I'm just not sure what I should attach it to.

Thanks!
 
Sponsored Links
  #2  
Old 12-18-15, 05:01 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,634
Received 515 Votes on 485 Posts
The nest cannot be run directly off that control. It uses an electronic switching section instead of a relay which means there is not enough current flow thru the R/W wiring to charge the nest.

You can purchase a 24vac transformer and power the nest directly.
Is this a boiler ? Is there another 24vac transformer there ?

Name:  Nest_backplate_with_wires - Copy.jpg
Views: 1632
Size:  21.1 KB

The red and white go to the controller.
The two blues are an alternate source or 24vac.
That means you'd need four wires to the stat.
 
  #3  
Old 12-18-15, 05:12 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,493
Received 33 Votes on 25 Posts
How many "extra" wires do you have? I try to avoid any questions on Nest thermostats but as I recall they can use a separate power supply. If you have two "extra" wires they could be used with a stand-alone (or plug-in) 24 volt AC transformer to supply the needed power to the thermostat.

You might ask the question in the thermostats forum.
 
  #4  
Old 12-18-15, 05:49 PM
Member
Thread Starter
Join Date: Feb 2015
Location: United States
Posts: 17
Received 0 Votes on 0 Posts
Thanks guys! The Nest does operate the control properly -- calls for heat are answered, etc., and the 7505 has 24vac power. The problem is that the Nest will occasionally "pulse" the control, presumably to steal more power, causing the boiler burner to start and stop. When I ran thermostat wire to the boiler last year I ran 5-wire cable, so I have 3 extras. You figure I can use two of those to wire in a separate 24v transformer and pick up the power for the nest that way? I'm looking at a Honeywell AT72 D 1006 at the store right now. Seems like it'll work, right?
 
  #5  
Old 12-18-15, 06:03 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,634
Received 515 Votes on 485 Posts
You only need 10va (watts) so that 40va one you spec'ed is fine.
 
  #6  
Old 12-18-15, 06:31 PM
Member
Thread Starter
Join Date: Feb 2015
Location: United States
Posts: 17
Received 0 Votes on 0 Posts
Great! How about the one that's already powering my doorbell? Can I just stack the two new wires on the 24vac terminals? Here's a picture:

Name:  IMG_1344.jpg
Views: 739
Size:  44.9 KB
 
  #7  
Old 12-18-15, 06:38 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,634
Received 515 Votes on 485 Posts
Yes.... you can use the outside two terminals for 24v.
 
  #8  
Old 12-18-15, 07:36 PM
Member
Thread Starter
Join Date: Feb 2015
Location: United States
Posts: 17
Received 0 Votes on 0 Posts
This worked great! Cost me $0. This after two straight days of the tech from the company that installed my boiler fumbling around in the basement without a clue. Much appreciated, man, you're a hero.
 
  #9  
Old 12-18-15, 08:02 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,634
Received 515 Votes on 485 Posts
You got that wired up quick. Glad to help.
 
  #10  
Old 12-19-15, 06:40 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Location: USA
Posts: 4,173
Received 25 Votes on 24 Posts
Might be a good idea to clean up that connection at that transformer,to much bare copper showing.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: