No water pressure in one zone
#1
Member
Thread Starter
Join Date: Jan 2016
Location: USA
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts
No water pressure in one zone
Hello all,
I have a Dunkirk boiler that I installed in the mid 90's. Everything has been fine up till last year. I had to replace the expansion tank and boiler fill valve. I have 3 loops. One is for the sidearm hot water heater. One is for the first floor. The last is for the second floor. Each loop has it's own circulator. First floor loop has all the mechanics, fill valve, pressure relief, expansion tank and such. The second floor loop has a air vent at the high point.
After the work last year I had air in the system on the second floor loop. This year the air is still there. Mainly can hear it when the circulator first comes on.
My main concern is I change the air vent earlier this year and there was no pressure when I took the old vent off. In the past there has been water skirting out when I had to replace this. The new one is a maidomist valve. I can press on the Schrader valve when the is on and air and or water will skirt out. But when the circulator is off the is no pressure on the loop. The boiler is holding 12 to 14 lbs of pressure. There is another gauge on the first floor loop and that is also holding at 12 to 14 lbs.
Anyone know why there is no pressure on the second floor.
I plan on putting a boiler drain on the second floor loop so I can purge that line better.
Thank you for any help.
ljc2tall
I have a Dunkirk boiler that I installed in the mid 90's. Everything has been fine up till last year. I had to replace the expansion tank and boiler fill valve. I have 3 loops. One is for the sidearm hot water heater. One is for the first floor. The last is for the second floor. Each loop has it's own circulator. First floor loop has all the mechanics, fill valve, pressure relief, expansion tank and such. The second floor loop has a air vent at the high point.
After the work last year I had air in the system on the second floor loop. This year the air is still there. Mainly can hear it when the circulator first comes on.
My main concern is I change the air vent earlier this year and there was no pressure when I took the old vent off. In the past there has been water skirting out when I had to replace this. The new one is a maidomist valve. I can press on the Schrader valve when the is on and air and or water will skirt out. But when the circulator is off the is no pressure on the loop. The boiler is holding 12 to 14 lbs of pressure. There is another gauge on the first floor loop and that is also holding at 12 to 14 lbs.
Anyone know why there is no pressure on the second floor.
I plan on putting a boiler drain on the second floor loop so I can purge that line better.
Thank you for any help.
ljc2tall
#2
Welcome to the forums.
I'm not the boiler pro but what I've done to purge an upper floor system is to shut the other zones off and raise the boiler pressure up to 20-25 psi to help get the water to the second floor.
After I get the air out I let water back out of the boiler.
The other guys will stop by an add their opinions to the mix.
I'm not the boiler pro but what I've done to purge an upper floor system is to shut the other zones off and raise the boiler pressure up to 20-25 psi to help get the water to the second floor.
After I get the air out I let water back out of the boiler.
The other guys will stop by an add their opinions to the mix.
#3
Member
Join Date: Dec 2013
Location: USA
Posts: 194
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I change the air vent earlier this year and there was no pressure when I took the old vent off.
The zone pump should be enough to move air in the system to the air separator.
Is this what you did.
Close automatic air vents, or they get plugged up.
Fill system -- all pumps OFF.
Open automatic air vent on boiler/ air separator.
Isolate system from water supply.
Monitor for pressure loss.
First floor loop has all the mechanics, fill valve, pressure relief, expansion tank and such.
All pumps should be on the supply side and pumping out into the system.
Expansion tank, reducing valve, air separator, all located on the suction side of pumps.
Air separator must be located in the primary system flow.
#4
Member
pressure
I wonder if your pressure gauge is accurate. There's a sticky at the top about checking your gauge. Also, did you check the air charge in the new expansion tank when you replaced it? Good luck, Steve
#5
Member
Thread Starter
Join Date: Jan 2016
Location: USA
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thank you for your responses. A little background on the system. Back in 1988 when I installed the system, it was an electric thermal system (OPUS). It came with all the piping and plumbing fixtures all put together. All I had to do was connect one end to the water tank and the other to the household baseboard heat. About 7 years later I replaced the water tank with a boiler. Everything was fine up till last year when I replaced the fill valve and expansion tank.
I never had problems with the automatic vent before. Actually had a plumber tell me to put one in back in 1988, to get rid of air in the second floor loop.
I believe that air is going back in the system from the automatic vent from the fact that there is no pressure in the line when the system is not circulating. I will close that vent off to see if it helps.
As I stated before I have 2 pressure gauges in the system (came pre-plumbed that way) one in the piping and one on the boiler. They both read the same , so I don't think the gauges are off.
I am just curious as to why there would be no pressure on the second story loop when there is pressure on the first floor loop.
I never had problems with the automatic vent before. Actually had a plumber tell me to put one in back in 1988, to get rid of air in the second floor loop.
I believe that air is going back in the system from the automatic vent from the fact that there is no pressure in the line when the system is not circulating. I will close that vent off to see if it helps.
As I stated before I have 2 pressure gauges in the system (came pre-plumbed that way) one in the piping and one on the boiler. They both read the same , so I don't think the gauges are off.
I am just curious as to why there would be no pressure on the second story loop when there is pressure on the first floor loop.
#6
Member
Join Date: Dec 2013
Location: USA
Posts: 194
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Because:
CounterPoint How Hydronic System Components Really Work [pdf]
[page 7, pdf] Water has weight!
And if you pump into the point of no pressure change the pressure out in the system drops.
[page 33, pdf] The Point of No Pressure Change.
CounterPoint How Hydronic System Components Really Work [pdf]
[page 7, pdf] Water has weight!
And if you pump into the point of no pressure change the pressure out in the system drops.
[page 33, pdf] The Point of No Pressure Change.
#8
Member
Thread Starter
Join Date: Jan 2016
Location: USA
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts
In the pdf you supplied it stated that the water supply should be turned off once the system pressure has been established.
So I turned off the supply valve today with 12 to 14 #'s of pressure in the system. The pressure remained the same all day. Thermostat called for heat later in the day. As the temperature rose the pressure rose to 24#'s. Out of curiosity I opened the supply valve and the pressure dropped immediately to 19#'s.
So I turned off the supply valve today with 12 to 14 #'s of pressure in the system. The pressure remained the same all day. Thermostat called for heat later in the day. As the temperature rose the pressure rose to 24#'s. Out of curiosity I opened the supply valve and the pressure dropped immediately to 19#'s.
#10
Member
Thread Starter
Join Date: Jan 2016
Location: USA
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Appears to be a lot of conflicting information out there. The pdf that I just read on here says the fill valve should be turned off after pressure is reached. The info on the taco fill valve I installed last year says it must be open all the time.
Other info has the air scoop in one place and the next info puts in another place. Same with circulator positions.
All I know is that my system worked fine until last year. Now I have air in the lines and can't seem to get rid of it.
Ground hog says we are going to have an early spring. So I may live with it for now and dig further into this spring.
Other info has the air scoop in one place and the next info puts in another place. Same with circulator positions.
All I know is that my system worked fine until last year. Now I have air in the lines and can't seem to get rid of it.
Ground hog says we are going to have an early spring. So I may live with it for now and dig further into this spring.
#11
Member
Join Date: Dec 2013
Location: USA
Posts: 194
Upvotes: 0
Received 0 Upvotes
on
0 Posts
What is confusing?
Did I post something confusing?
Air scoop is not a synonym for air separator, this is a Taco Inc AIR SCOOP [pdf] See Diagram on far right for proper installation of scoop. Inlet:18" minimum of straight pipe, full size of port, flow velocity should be 4 ft/sec. or less, and should see all of the system flow.
Did I post something confusing?
Air scoop is not a synonym for air separator, this is a Taco Inc AIR SCOOP [pdf] See Diagram on far right for proper installation of scoop. Inlet:18" minimum of straight pipe, full size of port, flow velocity should be 4 ft/sec. or less, and should see all of the system flow.
#14
Member
Thread Starter
Join Date: Jan 2016
Location: USA
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts
You have provided some good information. And I thank you for that. This is the conflicting information as I posted earlier
"Appears to be a lot of conflicting information out there. The pdf that I just read on here says the fill valve should be turned off after pressure is reached. The info on the taco fill valve I installed last year says it must be open all the time."
"Appears to be a lot of conflicting information out there. The pdf that I just read on here says the fill valve should be turned off after pressure is reached. The info on the taco fill valve I installed last year says it must be open all the time."
#15
Member
Join Date: Jan 2008
Location: Southeastern Pennsylvania
Posts: 3,290
Received 114 Upvotes
on
105 Posts
hi guys –
I’m not an expert, just know what I picked up on this forum. From what I remember it seems like there is no consensus out there from the pros about whether make-up water should be always ON or always OFF. I think I remember one point: if you have a leak and the water is always ON the leak is masked. But if you have a leak and the water is always OFF the boiler can overheat, the pressure rise, etc. I think there are other points also.
If I remember correctly, NJT on of the real experts here, doesn’t come down one way or the other. I can’t remember what the other experts here think. I haven’t looked but there may be some old threads here addressing that issue - if you can find them. My make-up water is always OFF and I have to admit it makes me a little nervous so I usually check my boiler pressure several times a day.
I’m not an expert, just know what I picked up on this forum. From what I remember it seems like there is no consensus out there from the pros about whether make-up water should be always ON or always OFF. I think I remember one point: if you have a leak and the water is always ON the leak is masked. But if you have a leak and the water is always OFF the boiler can overheat, the pressure rise, etc. I think there are other points also.
If I remember correctly, NJT on of the real experts here, doesn’t come down one way or the other. I can’t remember what the other experts here think. I haven’t looked but there may be some old threads here addressing that issue - if you can find them. My make-up water is always OFF and I have to admit it makes me a little nervous so I usually check my boiler pressure several times a day.
#16
Member
Join Date: Oct 2015
Location: United States
Posts: 12
Upvotes: 0
Received 0 Upvotes
on
0 Posts
In any closed heated hydro electric system with a leak the loss of water will cause a rise in temperature which will cause a corresponding rise in pressure. The leak needs to be fixed as it will only get worse but until then keep the water on.
#17
Member
Join Date: Jan 2008
Location: Southeastern Pennsylvania
Posts: 3,290
Received 114 Upvotes
on
105 Posts
David –
But I thought the problem with leaving the water always ON is that you won’t know you HAVE a leak that
For example if the leak is inside how would you know?
But I thought the problem with leaving the water always ON is that you won’t know you HAVE a leak that
needs to be fixed as it will only get worse
#18
Member
Join Date: Dec 2013
Location: USA
Posts: 194
Upvotes: 0
Received 0 Upvotes
on
0 Posts
How long has Bell & Gossett been doing reducing valves, etc?
Training Manuals - Xylem Applied Water Systems
[page 6, pdf] Pressure-Reducing or “Feed” Valve
[page 11, pdf] Something you may not know...
CounterPoint How Hydronic System Components Really Work [pdf]
TECHNICAL BROCHURE FHD-501A
Training Manuals - Xylem Applied Water Systems
[page 6, pdf] Pressure-Reducing or “Feed” Valve
. . .
______The pressure-reducing or “feed” valve’s job is to fill the system with
water and to keep that water under a few pounds of pressure at the top floor.
Your job is to figure out how much pressure you need in the basement to push
the water up to the top of the system and hold it there under pressure.
. . .
______The pressure-reducing or “feed” valve’s job is to fill the system with
water and to keep that water under a few pounds of pressure at the top floor.
Your job is to figure out how much pressure you need in the basement to push
the water up to the top of the system and hold it there under pressure.
. . .
. . .
Something you may not know...
______Here’s an important point. Don’t think of a feed valve as a safety device.
It’s not there to protect the boiler against a low-water condition. The only thing
that can effectively protect a hot water boiler from low water is a low water cut-off.
______A feed valve’s job is to set the initial system pressure. That’s it. For
safety’s sake, you should close the supply valve to the feeder once the system
pressure is established. This is important because a feed valve that’s left open can
mask a system leak. Systems leaks that go undetected can lead to air problems
and boiler corrosion problems.
______Remember, the only sure protection against a low water condition is a
properly maintained low water cut-off.
. . .
Something you may not know...
______Here’s an important point. Don’t think of a feed valve as a safety device.
It’s not there to protect the boiler against a low-water condition. The only thing
that can effectively protect a hot water boiler from low water is a low water cut-off.
______A feed valve’s job is to set the initial system pressure. That’s it. For
safety’s sake, you should close the supply valve to the feeder once the system
pressure is established. This is important because a feed valve that’s left open can
mask a system leak. Systems leaks that go undetected can lead to air problems
and boiler corrosion problems.
______Remember, the only sure protection against a low water condition is a
properly maintained low water cut-off.
. . .
CounterPoint How Hydronic System Components Really Work [pdf]
TECHNICAL BROCHURE FHD-501A