Leaking boiler pressure relief valve

I noticed a puddle on my floor coming from the boiler about a month ago and ignored it. I know thats bad but my previous puddle 3 yrs ago lead me to find a leaky boiler that I had to replace and I wasn't in the mood to push around and install another 650 lb monster again! Anyway to my pleasant surprise the boiler is fine and the leak is from the pressure relief valve - an Apollo 10408.

I followed the post here about checking the expansion tank and found my tank completely full - it must have ruptured. I replaced it with a previous one that still held air and have it at 12 lbs.

I 'flushed' the PRV for 5 seconds a few different times, but it still leaks. Should I assume it just 'bad'? Can it be taken apart and cleaned or fixed? Would it get damaged from a non-working expansion tank? If it comes with a new Burnham boiler then it is only 3 yrs old. Otherwise it would have been new in in 2001 when I rebuilt the boiler system.

Thanks!
 
Sponsored Links
  #2  
Old 03-04-16, 05:41 AM
Member
Join Date: Jun 2012
Posts: 919
Received 4 Votes on 4 Posts
If the pressure in the system is correct and lower then the relief valves blow off point, then yes, replace it.
 
  #3  
Old 03-04-16, 07:22 AM
Member
Join Date: Jan 2010
Location: North East Kingdom of Vermont
Posts: 2,533
Received 1 Vote on 1 Post
I'm just a Real Estate Broker; but I've tried cleaning/clearing a weeping Pressure Relief Valve several times; but met with success only once.

It seems that once they pop, there's seldom a way to get them to re-seat completely, as if the sealing gasket has been permanently dented, or some microscopic grit gets itself embedded in the gasket, preventing a tight seal.

I have one right now that's weeping about a cup of water per week (plus whatever evaporates), one drop at a time, and I'll replace it at the end of winter.

I don't know how to fully bench test one that I've cleaned before re-installing, and it is so frustrating to partially drain the boiler to do the replacement, I'd have to think long and hard before I trust my efforts at cleaning again.

I suppose, if you have exceptionally clean water, completely free of mineral deposits, cleaning is a possibility; but I think even the professionals are leery of doing the quick annual releases (flushes) to simply test the Valve as a safety feature.
 
  #4  
Old 03-05-16, 02:51 PM
Member
Thread Starter
Join Date: Feb 2008
Location: NY
Posts: 19
Received 0 Votes on 0 Posts
Well, I took a few mins to remove and inspect it. I installed this boiler so I have good valves all around so it wasn't a problem draining a small amount of water to take the valve out. There isn't really anything that can be taken apart though - it looks like the whole mechanism is pressed into the brass housing. So I flushed it and used some Lime-Away to clean it as best I could, then put it back on.

Success! (for now) No leak, but I'll keep my eye on it and replace if need be.

Thanks for your input.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: