Slantfin boiler-intermittent domestic hot water

slantfin boiler, lately it wont kick on for hot water, i can let leave the fauct open all day amd the boiler wont light, if i turn up house thermostat it will kick on every time.
 
Sponsored Links
  #2  
Old 09-03-16, 10:52 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,577
Received 415 Votes on 388 Posts
Welcome to the forums.

There should be a gray box on the front of the boiler. It is the aquastat. Its job is to maintain a certain low water temperature (+/- 140) in the boiler for domestic water and to limit the high water temperature in heating mode.

Can you shoot a few pictures and post them of your boiler setup. You could turn the power off to the boiler, remove the cover to the aquastat and post a pic of the insides of that too.

http://www.doityourself.com/forum/el...-pictures.html
 
  #3  
Old 09-04-16, 07:55 AM
Member
Thread Starter
Join Date: Sep 2016
Posts: 10
Received 0 Votes on 0 Posts
Name:  image.jpg
Views: 244
Size:  43.5 KBName:  image.jpg
Views: 244
Size:  43.5 KBName:  image.jpg
Views: 158
Size:  31.5 KB. zone valve callng for hot water, red light on?
 
  #4  
Old 09-04-16, 07:59 AM
Member
Thread Starter
Join Date: Sep 2016
Posts: 10
Received 0 Votes on 0 Posts
slant fin

Slant fin boiler. no hot water

Name:  image.jpg
Views: 325
Size:  34.2 KB
 

Last edited by PJmax; 09-04-16 at 11:42 AM. Reason: reoriented picture
  #5  
Old 09-04-16, 08:04 AM
Member
Thread Starter
Join Date: Sep 2016
Posts: 10
Received 0 Votes on 0 Posts
Name:  image.jpg
Views: 225
Size:  41.2 KB. aquastat on slantfin boiler
 
  #6  
Old 09-04-16, 08:10 AM
Member
Thread Starter
Join Date: Sep 2016
Posts: 10
Received 0 Votes on 0 Posts
Name:  image.jpg
Views: 271
Size:  43.5 KB. more pictures. santfin boiler
 
  #7  
Old 09-04-16, 11:45 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,577
Received 415 Votes on 388 Posts
You have a five zone control board. Do you know which zone is for the domestic ?

You need to see if that zone is being activated.
You may have a defective zone valve.
 
  #8  
Old 09-04-16, 01:32 PM
Member
Thread Starter
Join Date: Sep 2016
Posts: 10
Received 0 Votes on 0 Posts
yes, a 5 zone system, left zone on the panel is for domestic, it was green when i took the pict, why is the red lit also? 4 zones on the wall for heat, i dont know where the zone valve is for domestic, is it the same type of zone as heat!
 
  #9  
Old 09-04-16, 01:35 PM
Member
Thread Starter
Join Date: Sep 2016
Posts: 10
Received 0 Votes on 0 Posts
in the pict that shows the pipes and zone valves, there is a zone valve on left upper corner nearest to me, could that be it ?
 
  #10  
Old 09-04-16, 01:58 PM
Member
Thread Starter
Join Date: Sep 2016
Posts: 10
Received 0 Votes on 0 Posts
could it be the the thermostat in the boiler mate? however i have touched those wires together before and it didnt make a diff, and it does react to temp adjustment settings. the single top left zone valve does wire to the left circuit on the control board, but the location of the zone valve confuses me because it is before the heating zone valves on the main ht wtr line to the heating zones.
 
  #11  
Old 09-04-16, 02:35 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,577
Received 415 Votes on 388 Posts
The green light on means the zone is calling for heat. That means the tank stat is working.
The red light on below that means the zone valve is activated.

We just need to determine why when the zone is active and we don't have the burner.
If you disable that zone... pull off one stat wire... do you hear a zone valve close ?
 
  #12  
Old 09-04-16, 04:29 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,892
Received 25 Votes on 23 Posts
The end switch on the zone valve fires the boiler. You need to check the end switch leads with a multi-meter to verify..

If the t stat on the boiler mate is opening the zone, but boilers not firing, then that would be my best guess..

Probably will need to replace zone valve..

Sometimes they get corroded internally and cant open all the way to trip the end switch.
 
  #13  
Old 09-04-16, 08:44 PM
Member
Thread Starter
Join Date: Sep 2016
Posts: 10
Received 0 Votes on 0 Posts
yes, when i dosconnect a wire the zone valve closes, at one point the boiler lit, then shut rite back down. the green light red light are lit,faucet on for around 3 minutes and boiler dosent fite. water is hot, so it must have fired sumtime while we were gone. how long normally does it take to fire the boiler when using the ht water? thx for your efforts
 
  #14  
Old 09-04-16, 11:08 PM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 17,892
Received 25 Votes on 23 Posts
It will open the zone and fire when the t stat gets below set point...

Here

Lower t stat under gray cover and see if zone valve opens.. It should call for heat too. If no zone valve faulty I would say...

[ATTACH=CONFIG]70465[/ATTACH]
 
Attached Images  
  #15  
Old 09-05-16, 09:17 AM
Member
Thread Starter
Join Date: Sep 2016
Posts: 10
Received 0 Votes on 0 Posts
it was the zone valve, thank you, funny thing , plumber been here 2 times in last month( his mom is our neighbor) and he didnt fix it. luckly i had a spare laying around. thx again
 
  #16  
Old 09-05-16, 11:56 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,577
Received 415 Votes on 388 Posts
Always good to have a spare zone valve available.

Thanks for letting us know the outcome.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: