Replace Honeywell L8148a with Hydrostat 3250

I have been reading posts about the 8148 relay failing by solder cracking and am pretty sure That is exactly my problem.

My system was not making hot water and I discovered the remote HW tank circulator was working and the boiler was firing to settings but the main circulator was not coming on for HW or radiation calls for heat.

I hooked a separate 120V to the main circulator [disconnected 8148 at circulator] and voila !hot water and main circulator function.Luckily I have a bypass to my HW heat exchanger that is always partially open so no chance of killing circulator[I hope?]

My aquastat is so poorly placed that it is a major PITA to dewire it to allow me to resolder the relay connections. It doesn't help that it is on a 20A circuit and has 12 gauge wires.

I am considering replacing the 8148 with a Hydrolevel 3250 plus for the main reason that it can be mounted remotely [and hoping for some predictive/thermal logic savings] I have seen at least one post complaining of catastrophic failure of the 3250[spraying steam/water when it heated over limit. I do have a separate overlimit safety,I assume I can keep it ]

Anyone [looking at you NJT] think this might be worth it?

My system

LAARS D-MAX [steel,low volume boiler operated cold start,direct vented]
TACO ZVC 406 zone valve controller
Remote HW tank with bronze circulator
TACO mixing valves supplying in floor radiantand towel bars,first floor
Baseboards on second floor
I designed/built this system myself to approximate a System 2000 [without their control board or prices]
I am in upstate NY

Thanks for any advice
 
Sponsored Links
  #2  
Old 09-24-16, 10:54 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,706
Received 345 Votes on 323 Posts
Welcome to the forums.

NJT has left the board.
On the surface that Hydrolevel looks like a good replacement. Since I haven't worked with that piece I can't offer any opinions but another member should be able to add some info.

I do have a separate overlimit safety,I assume I can keep it
I definitely recommend keeping it in the system.
 
  #3  
Old 09-24-16, 10:58 AM
Member
Join Date: Jan 2010
Location: North East Kingdom of Vermont
Posts: 2,533
Received 0 Votes on 0 Posts
I have had 8148s (and 8124s) fail on me; but it's usually been the points or contacts that got burnt or oxidized or corroded, and I bought myself some time by filing them to achieve a more serious contact. They've usually died on me completely when the electro-magnet winding burned/melted. I guess Sid Harvey re-builds them by replacing that relay.

I've never had the circuit board solder crack or melt; but I guess that is worth checking out.

Over the past 10 years, I have relied on a digital Honeywell L7224U and haven't had any such issues.

My thought is that I'd first try to clean up the contacts before attacking the circuit board.
 
  #4  
Old 09-25-16, 11:35 AM
Member
Join Date: May 2006
Location: upstate New York
Posts: 397
Received 0 Votes on 0 Posts
I've been using the 3250 for several years with no problems. I have heard of others with trouble though. Good luck, Steve
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: