General questions about removing air from the system

I bled out the air from my system last night. At one point my pipes were banging around like crazy. It made me highly nervous as it did not sound or feel right. I have bled air out before and have not seen this behavior. What may have caused this?

Also.. my expansion tank kept gurgling. I could clearly hear air in it rising to the top. Its mounted with the air pressure valve facing up/"on the top". After this my pressure relief valve starting leaking. Wondering about the gurgling noise. I don't think this is normal? Is it a symptom of air being trapped? Should I be concerned? Ignore? I will check the pressure on the valve. Thanks thanks thanks.
 
Sponsored Links
  #2  
Old 10-20-16, 08:28 AM
Member
Join Date: Oct 2008
Location: USA
Posts: 2,877
Received 5 Votes on 5 Posts
What is the boiler pressure? The relief valve will lift at 30 psi, so it appears that your expansion tank has lost its air charge. You will need to cool down and depressurize your system and then, and only then, pump up the bladder side to 12-15 psi. You can't check the air charge without first depressurizing the system.

The best time to have done this was when you had the system depressurized to replace the pump - but, whatever.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: