Madness with Weil McClain CVT gold

Reply

  #1  
Old 12-11-16, 12:08 PM
Member
Thread Starter
Join Date: Dec 2016
Posts: 1
Madness with Weil McClain CVT gold

I have been battling this thing for over a month. I've gotten it pretty well fixed but this last issue has me stumped. My understanding is that for space heat the three way valve actuator drops and pushes down on the valve to allow water to circulate through the house and heat. In my case it is the opposite. With the actuator in place the control board does try to do just that, but with the valve/actuator in the down position water doesn't flow to the baseboards. The circulator will be running the boiler up to temp and the baseboards cold. As soon as I remover the actuator and the valve pops up the baseboards get as hot as can be.

The install is from 2007 or 2008. I see there was a service bulletin that required the three way valve to be spun 180 degrees. Based on serial number that does not apply to my unit. I did just install a new cartridge in the three way valve as it wass weeping. Is it possible that the cartridge is for the updated valve orientation.

In any case my boiler will not heat the house with the actuator on. With it off I assume I'll be in short supply of domestic hot water as that is the function of the 3 way. To make domestic regardless of space heat demand so as not to get a cold shower etc.

Thanks in advance.
 
Sponsored Links
  #2  
Old 12-11-16, 12:25 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 51,388
Upvotes Received: 208
Welcome to the forums.

You've left us the boiler model but nothing on the valves you're working with.
 
  #3  
Old 12-11-16, 03:34 PM
Member
Join Date: Nov 2011
Location: USA
Posts: 401
Do you mean Weil Mclain CGt? The CGt comes with the kind of 3-way valve you seem to be describing.

I don't know for sure so don't quote me, but I believe the "default" position for that kind valve is to allow hot boiler water to flow through the system supply piping, and out to the emitters, and then back through the return piping into the boiler.

The "event" that triggers the valve to change position occurs when the boiler water is too cool to provide domestic water from the coil. Upon such event,
the valve changes position and closes off the system return water port, which causes all the hot boiler water to be diverted directly back into the boiler instead of going through the heating loop.

It would seem a little strange to me that the valve would need to be "actuated" in order to remain in the default position. I would think it more likely that the opposite is true....that the valve is only actuated when the "event" occurs.

Obviously it's critical to install the valve in the correct position. Maybe you have some kind of installation/piping issue.

P.S. Do you have the installation/operation manual for the boiler?
 
  #4  
Old 12-11-16, 03:46 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 51,388
Upvotes Received: 208
Ahhh...... that makes more sense..... CGT.

There are a few manuals floating around but this is a good one.
weil-mclain/field-file/cgt-manual_1.pdf
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes