Boiler stopped working: Honeywell L4103 ?

I have a fuel oil boiler that has stopped working. Of course it is friday and this is a rural area so Monday is the earliest I can get anybody out. Of course it is snowing and chilly.. This boiler produces hot water for the house and for radiant heating.

I don't seem to be getting power to the Beckett R7184 B 1032. So I looked further back at the Aquastat. I put a voltage detector on one side of the high limit switch (HoneyWell part T497A 3859) and I see voltage going in. But nothing coming out. Maybe that is supposed to be or not.

Can I anybody help me track down why I might not be getting power to the Beckett?

Please..

All typo's I am blaming on my ice cold fingers..
 
  #2  
Old 04-08-17, 10:24 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,928
Received 3,947 Upvotes on 3,540 Posts
Welcome to the forums.

I moved your thread to the boiler forum.

You should be using a voltmeter or voltage tester to check for power. You need to confirm you have neutral as well as hot.

I'm not sure how the high limit switch is wired into your system but it's not part of the aquastat.

You can post some pictures of the wiring so we can see what you see.
http://www.doityourself.com/forum/el...-pictures.html
 
 