Boiler not operating when call for heat

Reply

  #1  
Old 07-26-17, 08:22 PM
F
Member
Thread Starter
Join Date: Jul 2017
Location: USA
Posts: 1
Received 0 Votes on 0 Posts
Boiler not operating when call for heat

I have a Utica Boiler that feeds 5 zones. The boiler does not fire with a call for heat for the hot water tank. The solenoid operates, but system does not run. I manually operated each of the remaining 4 zones to see if maybe I have a bad HW solenoid, but had the same result..... no circ pump, no fuel pump and no burner action.

I removed the cover to the Honeywell L8148A Aquastat box. I manually moved the contactor relay and immediately the circ pump starts, then after about 5-7 secs the fuel oil pump starts and then burners start. I release the relay, everything shuts down.

I jumpered the TT points and the system started.

I have verified 120v at circ and boiler connectors and 26VAC at the TT points, both in the Aquastat.

System pressure is 30#, so this is not a low water pressure issue.

It his highly unlikely that all 5 solenoids would fail (4 that have not been used since April). So I do not believe it has anything to do with the 24 VAC side.

I am apt to replace the Aquastat, but when I jumper out the TT, all is fine.

Thoughts/suggestions?

Thank you!
 
Sponsored Links
  #2  
Old 07-26-17, 09:00 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,772
Received 1,192 Votes on 1,103 Posts
Welcome to the forums.

but when I jumper out the TT, all is fine.
Ok.... so it's not the aquastat.

Do you have a zone control system or just five zone valves with a spaghetti mess of wiring ?

I'm guessing no zone controller which means a lot of wiring.
My first thought is a second defective 24vac transformer. This transformer runs the valves. A quick confirmation is..... is the HW zone valve open ?

My second thought is a broken wire between the zone valves and TT.
My third thought is there a safety sensor open in the TT line.

For a tech this would be an easy repair. For us it will be hard to tell you what to check.
Do you have a voltmeter ?

Can you take a few pics of the wiring and post them here.
http://www.doityourself.com/forum/el...-pictures.html

System pressure at 30psi on a cold boiler is way to high. It should be closer to 12-15psi. You may need to check into the expansion tank pressure. There is a sticky at the top of the forum that describes the testing. This isn't your current problem but will need to be looked into.
 
  #3  
Old 08-02-17, 04:57 PM
S
Member
Join Date: May 2006
Location: upstate New York
Posts: 402
Received 0 Votes on 0 Posts
When the zone valve opens fully, it closes an end switch which signals the aquastat to turn things on. On Honeywell zone valves, the 2 red wires go to the end switch. The end switch is not replaceable, but the end switch, motor, and mounting plate are available as a unit, so you don't have to replace the whole zone valve (no messing with the piping). Supplyhouse.com is one place to get parts. Agree with PJ that pressure is too high, but that's another problem. Good luck, Steve
 
  #4  
Old 08-02-17, 09:05 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,772
Received 1,192 Votes on 1,103 Posts
Thanks for the additional info Steve. Since he tried each zone valve manually... a defective end switch is probably not the problem here.

We were waiting to hear back from the OP. He seems to have forgotten he posted here.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: