Aquastat for indirect HWH

Reply

  #1  
Old 09-08-17, 12:53 PM
Member
Thread Starter
Join Date: Jan 2014
Location: USA near Boston, MA
Posts: 650
Likes Received: 15
Aquastat for indirect HWH

Can I use a Honeywell L8124 A,C as the control for an indirect WH instead of an L4080B? I will wire one of the outputs (boiler or circulator) to the thermostat terminals in a TACO 4-zone control panel that will control a separate circulator and provide priority to the WH.
 
Sponsored Links
  #2  
Old 09-08-17, 01:11 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 50,990
Likes Received: 162
I suppose.

The L4080B is just a standalone high limit thermostat.
The L8124AC is a full aquastat and will require AC power to operate.
 
  #3  
Old 09-08-17, 01:21 PM
Member
Thread Starter
Join Date: Jan 2014
Location: USA near Boston, MA
Posts: 650
Likes Received: 15
Thanks for pointing out about the AC power. If I thought it through I would have realized that the relay needs power to operate. I was just thinking of a cost saving since I have an L8124AC on hand. Even though I do my own wiring the time and effort as well as adding a possible point of failure is not worth it. I'll go with the L4080B.
 