OLD boiler relay L8048F
Old 11-02-17, 09:39 PM
Hello, I have an old A.S. Hydronic boiler, it has a Honeywell AQUASTAT relay type L8048F. Have had to replace one zone valve (2 zones total) as well as some other parts, pipes, etc. wiring was old and jumbled that went to zone valves and came from 24 volt transformer and from relay, trying to find how to wire the zone valves properly. Any ideas? Where to find schematics, etc.?
Old 11-02-17, 11:27 PM
Received 1,525 Votes on 1,408 Posts
Welcome to the forums.
Old boiler with old aquastat.
The wiring for 2 zone valves, 1 transformer, 2 thermostats and an aquastat is fairly straightforward.
What is needed is what type of zone valve...... 3 wire...... 4 wire..... ?
Old 11-03-17, 07:41 AM
Four wires on both zone valves
zone #1 is a new HONEYWELL, 2 yellow and 2 red (motor and switch respectively)
zone #2 is an old Honeywell with terminal screws on one end. I do know which terminals(wires) go to motor and switch.
The main trouble I am having is with how to wire it all correctly.
there is a 24 v. transformer from the house power, and terminal screws on the AQUASTAT (listed below)that read “24 V thermostat” 3 screws total, and two are connected with a jumper.
Old 11-03-17, 10:12 AM
In the diagram I colored the screw terminals to match a standard 4 wire valve. The fifth terminal (TH-TR) is just a splice point. It is not connected to anything inside the valve. It does not need to be used. The transformer is AC and has no polarity or R and C markings.
Name:  zv - Copy.JPG
Old 11-03-17, 12:18 PM
Yes, very helpful, will use that when I get to wiring.
the other part I am struggling with is the AQUASTAT and how/where and what wires go to the terminals on it that say 24v thermostat? Here it is in the photo upper left terminals it is the red and white wires
Old 11-03-17, 02:26 PM
The aquastat has TT terminals that go to the red wires on the zone valves. There is no power connected to those red wires. The aquastat supplies its own power to operate.
On the aquastat will be two terminals labeled B1 and B2.
B1 is hot to the burner and B2 is the neutral to the burner.
Then there is C1and C2. C1 is hot to the circulator and
C2 is the neutral to the circulator.
I don't see any pictures.... How-to-insert-pictures
Old 11-03-17, 02:47 PM
Hello, have been trying to figure out how to load photos most of the day, I did manage to copy/paste one, guess it did not work.
the C1 C2 B1 B2 you mentioned are wired correctly, did not have to mess with those. The terminals I am talking about, it says above them 24V thermostat then one is labeled TV, T, and W. With a jumper that goes in between T and W, which can be removed.
I will keep trying to get the photos loaded.
thanks for the help
Old 11-03-17, 02:56 PM
Relay photos
Old 11-03-17, 03:44 PM
Go the "go advanced" tab at the bottom of the page. Once you're in the advanced screen click on the paperclip. You'll see browse. Click on that and it will be your computer. Find the pic you want and click upload. You should see your file at the bottom of the upload page. You can click on browse again for a second picture and so on. If your pictures are from a phone they may be gigantic.... like 3k-4k file size and 2000x2000 pixel size. The board cannot resize pictures that are that large.
Old 11-03-17, 04:15 PM
Size:  17.7 KBName:  B0823601-D097-4DC5-A7BB-B20B74E4D859.jpg
Size:  18.4 KBSee if these help