Zone valve problem

I have Honeywell zone valves on my system.woke up this morning and thermostat said 60 dg,set on 68.I went down and the zone valve motor was not engaging switch,I replaced motor and worked.
I went out got home and thermostat read 62 dg,turned thermostat up to 68 and checked zone valve and it was ok.Any help would be appreciated.
 
  #2  
Old 02-06-18, 08:19 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,159
Received 3,627 Upvotes on 3,251 Posts
Welcome to the forums.

What do you mean you checked it and it was ok ?
Was the valve open ?

You had a defective motor, you replaced it and now the valve still isn't working right.
The valve may be sticking internally.
 
  #3  
Old 02-07-18, 07:56 AM
D
Member
Join Date: Apr 2014
Location: us
Posts: 1,318
Received 102 Upvotes on 96 Posts
Sometimes the brass gears wear. Midway thru travel gears cease to mesh fully and slip. Then switch may not activate

Test by putting 24 VAC on motor and watch is gears closely. Can also put ohm meter on switch to confirm closure when valve is open.

Putting valve in "manual open" position should also close switch.

If Microswitch is bad many electronic supply places have them.

http://www.skycraftsurplus.com/microswitches.aspx
 

Last edited by doughess; 02-07-18 at 09:30 AM.
 