Replacing a pressure relief valve

Older furnace needs to have its pressure relief valve replaced.

The existing valve is rated for 550,000 BTU/Hr but all the ones I have found online seem to cap at 510,000. I assume since the furnace output 90,000 BTU/Hr that the ones rated 510k are fine?

Is there a preferred brand I should look for based on quality?

Lastly, the expansion tank looks original so its gotta be 40 or so years old. Is it wise to replace that as well while we're at it.

Thanks
 
Attached Images  
Sponsored Links
  #2  
Old 09-25-18, 10:45 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,616
Received 514 Votes on 484 Posts
Thread moved to the boiler forum. A furnace is hot air.
 
  #3  
Old 09-26-18, 07:16 AM
Member
Join Date: Oct 2008
Location: USA
Posts: 2,925
Received 8 Votes on 8 Posts
Anything over the boiler input rating will be OK. It's 112,500 Btu/hr, not 90,000. The most common brand is Watts, but I wouldn't worry too much.

Is it a bladder-type expansion tank or a conventional, horizontal tank? A bladder-type tank looks like a propane cylinder for a BBQ grill. A conventional tank will last indefinitely, a bladder tank will eventually fail and will require checking and replenishing the air periodically. There is a sticky on this forum that tells how.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: