Weil McLain Boiler Temperature Control
#1
Member
Thread Starter
Join Date: Dec 2018
Location: United States
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Weil McLain Boiler Temperature Control
I'm using a Weil Mclain Ultra Series 2 boiler for my driveway melt. How do I adjust the thermostat?
After very cold nights (below 10 degrees) I have to reset my boiler. I'm afraid the glycol mix in the tubing is freezing and the boiler shows error codes. I'm hoping the solution is raising the low setting on the boiler, currently set at 38. Does this sound correct? If so, how do I do this?
thanks!
After very cold nights (below 10 degrees) I have to reset my boiler. I'm afraid the glycol mix in the tubing is freezing and the boiler shows error codes. I'm hoping the solution is raising the low setting on the boiler, currently set at 38. Does this sound correct? If so, how do I do this?
thanks!
#2
I'm using a Weil Mclain Ultra Series 2 boiler for my driveway melt. How do I adjust the thermostat?
After very cold nights (below 10 degrees) I have to reset my boiler. I'm afraid the glycol mix in the tubing is freezing and the boiler shows error codes. I'm hoping the solution is raising the low setting on the boiler, currently set at 38. Does this sound correct? If so, how do I do this?
thanks!
After very cold nights (below 10 degrees) I have to reset my boiler. I'm afraid the glycol mix in the tubing is freezing and the boiler shows error codes. I'm hoping the solution is raising the low setting on the boiler, currently set at 38. Does this sound correct? If so, how do I do this?
thanks!
Im sure the ODR is set up with the boiler and also should have some type of mixer valve on the snow melt system.
But boiler temps should reach 180f of so in cold conditions if ODR parameters in the control are set up correct.
Glycol will not freeze afaik but will slush up.
Pics?
#4
Member
Thread Starter
Join Date: Dec 2018
Location: United States
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It's a separate boiler from the household supply.
I'm getting error code E 36 now. Any ideas what that means? Could the boiler, which is in the garage, be too cold?
thanks!
I'm getting error code E 36 now. Any ideas what that means? Could the boiler, which is in the garage, be too cold?
thanks!
#5
Member
Join Date: Jan 2008
Location: Southeastern Pennsylvania
Posts: 3,151
Received 102 Upvotes
on
94 Posts
https://www.weil-mclain.com/sites/de...pplement_1.pdf
Page 32 of the above manual says this about E 36:
This manual describes that sensor:
https://www.weil-mclain.com/sites/de...2-manual_1.pdf
Page 32 of the above manual says this about E 36:
36 Outlet water temperature sensor
open circuit.
open circuit.
https://www.weil-mclain.com/sites/de...2-manual_1.pdf
7. Outlet water temperature sensor
This sensor monitors boiler outlet water temperature (system supply).
The control module adjusts boiler firing rate so the outlet temperature is
correct.
This sensor monitors boiler outlet water temperature (system supply).
The control module adjusts boiler firing rate so the outlet temperature is
correct.