Curious Piping on a Boiler


  #1  
Old 12-16-18, 12:08 AM
M
Member
Thread Starter
Join Date: Dec 2018
Location: USA
Posts: 16
Received 1 Upvote on 1 Post
Question Curious Piping on a Boiler

I was working on a friends gas-fired boiler today. He said the pressure relief valve opened and won't stop running. A new 30psi relief valve and draining the water-logged expansion tank was a quick fix for a change. As I was looking at his setup I noticed a piping configuration that has me puzzled. He has 3 zones. Just after the circulators there are smaller diameter pipes, with valves, that connect to the returns on each zone. What is the purpose?
Also, what should be the static pressure be on a boiler? When the system cools the pressure drops to 0psi. I think the pressure should be higher than that, but I'm having a brain fart.

Thanks!
 
  #2  
Old 12-16-18, 04:03 AM
S
Member
Join Date: Jan 2017
Location: USA
Posts: 447
Upvotes: 0
Received 14 Upvotes on 11 Posts
The required cold water system pressure is determined by the height of the highest radiation down to the pressure gauge (if it is reading the correct pressure) multiplied by .433, plus an additional 2 psi pressure above that reading. For example; if the measurement as previously described was 25 feet then the cold pressure would be about 12.8 or 13 psi when the number is rounded up. (25 X .433 = 10.8 + 2 = 12.8 or 13) However in the boiler business PRV controls are usually factory preset to 12 PSI , which is OK for most installations. When there was doubt we would use 12 psi for a 1 story home and 15 for a 2 story home and 20 psi for a 3 story home. as long as the expansion tank was sized correctly.
 
  #3  
Old 12-16-18, 10:17 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,535
Received 3,485 Upvotes on 3,128 Posts
Welcome to the forums.

Pictures of your boiler and piping would be very helpful..... How-to-insert-pictures
 
  #4  
Old 12-16-18, 12:01 PM
poorplmbr's Avatar
Member
Join Date: Feb 2003
Location: long island ,new york
Posts: 307
Received 15 Upvotes on 14 Posts
Curious piping

Sounds like system bypass piping. It allows hot supply water to mix with cold return water so as to not shock the boiler and cause condensation or worse crack the boiler
 
  #5  
Old 12-16-18, 04:56 PM
M
Member
Thread Starter
Join Date: Dec 2018
Location: USA
Posts: 16
Received 1 Upvote on 1 Post
I do have pictures, but I can see the detail really doesn't show enough detail. I'll get new pictures either tomorrow or Tuesday. Until then...
 
  #6  
Old 12-19-18, 06:18 PM
M
Member
Thread Starter
Join Date: Dec 2018
Location: USA
Posts: 16
Received 1 Upvote on 1 Post
I didn't forget the pics. I took new pictures, but they don't identify the layers properly. I'm making a diagram to go along with the pictures. Hopefully I will have this done tomorrow.
 
  #7  
Old 12-20-18, 09:27 PM
M
Member
Thread Starter
Join Date: Dec 2018
Location: USA
Posts: 16
Received 1 Upvote on 1 Post
Here is the diagram I promised. I also included a picture so that you can see the plumbing rats nest.
 
Attached Images   
  #8  
Old 12-21-18, 07:36 AM
B
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 2,778
Received 245 Upvotes on 217 Posts
You need shut-off valves in the green and blue loops to isolate the loops for bleeding one loop at a time. Also the expansion tank should be relocated to the manifold or common return pipe (between furnace and first junction) to best sense system volume. Don't know why the bypass valves are installed since normally they all must be shut off to prevent flow problems whenever at least two loops are operating.
 
  #9  
Old 12-22-18, 07:21 AM
poorplmbr's Avatar
Member
Join Date: Feb 2003
Location: long island ,new york
Posts: 307
Received 15 Upvotes on 14 Posts
As I stated, system by-pass if, say the green zone was running and the boiler was already hot, and then the red zone kicked on, and had been off for a while , it would bring cold water into a hot boiler. The by-pass would allow tempered water to return to the boiler rather than very cold which could be detrimental to the boiler.
 
  #10  
Old 12-23-18, 12:18 AM
M
Member
Thread Starter
Join Date: Dec 2018
Location: USA
Posts: 16
Received 1 Upvote on 1 Post
Now I see what you're talking about, poorplmbr. That makes perfect sense. I'll have to look at what position the valves are in. Beelzbob, I did notice that tank's position once I made the drawing and was thinking it was in the wrong spot, but since it was working, i figured I was thinking about it too hard. It's reassuring to find out my suspicions were correct. Thank you both for your your input!
 
 