Boiler Not Heating

Reply

  #1  
Old 02-21-19, 01:27 PM
Member
Thread Starter
Join Date: Feb 2019
Posts: 4
Boiler Not Heating

My natural gas boiler has stopped turning on. The pilot will stay lit, but the flames wont come on. I've tried setting the zone valve to manual open but that doesn't achieve anything. I've also check to make sure the breaker for the boiler wasn't tripped in my breaker box. I'm guessing something shorted on it? But I'm a little loss on where to check. I do have a multimeter.

Below are pictures of the boiler


Name:  b1.jpg
Views: 113
Size:  81.6 KB


Name:  b2.jpg
Views: 111
Size:  40.3 KB


Name:  b3.jpg
Views: 110
Size:  50.9 KB


Name:  b4.jpg
Views: 106
Size:  74.3 KB
 

Last edited by PJmax; 02-21-19 at 03:57 PM. Reason: reoriented/enlarged pics
Sponsored Links
  #2  
Old 02-21-19, 04:02 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 50,954
Likes Received: 155
Welcome to the forums.

That boiler looks like it could use a good cleaning.
They should be professionally cleaned every couple of years.

With your meter.... check the two transformers for 24vAC. They may be marked R and C.
Is this a cold start boiler or did it stay heated all the time ?
That thermostat looking device mounted to the pipe is for overheating protection. Check that for 24vAC. There should be 0v on the two terminals.
 
  #3  
Old 02-21-19, 04:31 PM
Member
Join Date: Oct 2008
Location: USA
Posts: 2,853
Likes Received: 3
Based on your post - you need to hire an experienced professional. Someone whose references you've checked - not just out of the yellow pages.
 
  #4  
Old 02-21-19, 05:35 PM
Member
Thread Starter
Join Date: Feb 2019
Posts: 4
pjmack The one on the side of the system, shown in the second picture is reading 24 volts. The one shown in picture three is showing 0 volts. Did you want me to read the voltage of the one in picture three or a different one?
 
  #5  
Old 02-21-19, 06:02 PM
Member
Join Date: Nov 2012
Location: USA
Posts: 3,760
Likes Received: 7
Hi, at the Tstat jump R to W and see if it fires up.
Geo
 
  #6  
Old 02-21-19, 11:48 PM
Member
Thread Starter
Join Date: Feb 2019
Posts: 4
Nothing, any other ideas?
 
  #7  
Old 02-22-19, 04:38 AM
Member
Join Date: Nov 2012
Location: USA
Posts: 3,760
Likes Received: 7
That boiler definitely requires some professional attention, what is hanging out in the top picture,what is that blue thing?
Geo
 
  #8  
Old 02-22-19, 09:40 AM
Member
Join Date: Oct 2013
Location: United States
Posts: 2,687
Likes Received: 8
You should have 24V at your stat when not calling for heat and 0 Volts when it is calling. If you do not get these readings then you must trace your circuit back to the transformer that feeds the stat and find out why.
 
  #9  
Old 03-08-19, 12:14 PM
Member
Thread Starter
Join Date: Feb 2019
Posts: 4
If I have 24 volts when it’s not calling for heat and my transformer on the side of the unit is displaying 24v what should I check on the unit next?
 
  #10  
Old 03-08-19, 12:39 PM
Member
Join Date: Nov 2012
Location: USA
Posts: 3,760
Likes Received: 7
With the Stat calling check for 24 volts at the gas valve.
Geo
 
  #11  
Old 03-08-19, 02:48 PM
Member
Join Date: Oct 2013
Location: United States
Posts: 2,687
Likes Received: 8
Call for heat and check voltage at stat. Should read o volts. if not you can try jumping stat wires to see if boiler comes on. If not you are going to have to trace the circuit for 24V all the way to the gas valve. What do have for zone valves. Pics of the ZV and wiring from the ZV to where it ties into the boiler would be helpful.
 