Want opinion on leaving stuck open zone valve in place

I have hot water baseboard heat in my home home with three zones - 1st floor, 2nd floor and basement. the basement is partially finished and under served with a short run of baseboard on one wall. It manages to keep the area at about 62 - 65 degrees in very cold weather. If I set the thermostat to 68 or above the boiler seemed to stay on constantly.

At the end of last years heating season the zone valve for the basement started sticking open even when the thermostat reached set temp. I went downstairs and found the temp reading at 68 and a bit higher making it more comfortable. I figure that even though that thermo is not calling for heat, since the zone valve is stuck open, when 1st or 2nd floor calls for heat , hot water is also being pumped through the basement.

I'm experienced in replacing zone valves so its no problem for me to do it but I'm think maybe I should keep it this way to keep the basement warmer. It ran this way for about 3 weeks before I shut down the system in the spring. It didn't seem like the system was struggling to warm the other two floors. Any opinions? It makes sense for me to replace the valve now before I turn on the system for the winter.

Thanks for any input.
 
Sponsored Links
  #2  
Old 09-10-19, 11:21 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,608
Received 339 Votes on 317 Posts
Leaving the valve open and receiving some residual heat from a heat call for zone 1 or 2 should be ok.

One problem.... is the circulator tied to that zone valve ?
You wouldn't want that to run continuously.
 
  #3  
Old 09-10-19, 11:53 AM
Member
Thread Starter
Join Date: Jul 2002
Location: Staten Island, New York
Posts: 199
Received 0 Votes on 0 Posts
Thanks for the quick reply.
I didn't think of that. I will try to check that tonight and will report back.

That "little guy" that pops up on your shoulder when you try something like this had been telling me to put it back the way it is designed to work!
 
  #4  
Old 09-13-19, 02:33 PM
Member
Join Date: Mar 2009
Location: USA
Posts: 675
Received 1 Vote on 1 Post
You might able to replace the motor only. Depending on the brand, it's not that hard.
There probably a video on U tube. Even if you have to buy the whole unit, which is not much more, and the motor slips off, one or two screws. Make sure it goes on the same way as the old power head.
Sid
 
  #5  
Old 09-14-19, 06:43 AM
Member
Thread Starter
Join Date: Jul 2002
Location: Staten Island, New York
Posts: 199
Received 0 Votes on 0 Posts
Thank you pjmax and sidny for the info.
I ran the system yesterday morning and the thermostat reached request temp. And the contact arm did not stick, the spring pulled the arm and the valve worked as it should. tried it on and off a few times. I guess the "rest" over the summer has it working correctly.
I did watch one video on youtube that give a good explanation of the operation and it looks like if the contact is stuck on that the circulating pump would constantly be energized so I'm going to replace the valve.
I did consider switching the electronics off of the new valve as you suggest but it's not a big deal for me to open the piping and replace the entire valve.
 
  #6  
Old 09-15-19, 07:48 AM
Member
Join Date: Apr 2014
Location: us
Posts: 607
Received 4 Votes on 4 Posts
It would help to know the brand and model of valve.
 
  #7  
Old 09-18-19, 09:02 PM
Member
Thread Starter
Join Date: Jul 2002
Location: Staten Island, New York
Posts: 199
Received 0 Votes on 0 Posts
As suggested by sidny, I found the Honeywell replacement motor for the valve and installed it so I didn't have to open up the plumbing part. Simple to replace in about two minutes and the valve is working as it should.
Thanks for the advice.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: