Burners won’t come on

Hi have a Burnham Gas boiler series 2a pilot light goes on but burners won’t so far changed gas valve ,thermo coupler , roll out switch ,damper and still not working thermostat works we bypassed it and still burners won’t come on has electricity going thru breaking our heads here what could it be??
 

Last edited by PJmax; 10-20-19 at 03:25 PM. Reason: removed link
  #2  
Old 10-20-19, 03:12 PM
G
Member
Join Date: Oct 2008
Location: USA
Posts: 2,604
Received 28 Upvotes on 27 Posts
Don't throw any more parts at it without troubleshooting to identify the cause. If you have a multimeter (and know how to use it) and an electrical schematic for your system, trace out the wiring - start at the thermostat and work toward the gas valve, and find out where the 24-V is being lost. If this isn't something you can do, then call a pro whose references you've checked.

Good luck.
 
  #3  
Old 10-20-19, 03:27 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,816
Received 3,922 Upvotes on 3,518 Posts
Welcome to the forums.,

There is no thermocouple on a intermittent ignition furnace.
Your problem is probably going to be the combination spark/flame sense rod.

There was a link in your post. Was that supposed to be to pictures ?
 
  #4  
Old 10-20-19, 05:00 PM
L
Member
Thread Starter
Join Date: Oct 2019
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes did use multimeter traced out the wiring and the problem
from the transformer followed the wires to the damper to see if the damper is opening and it is checked and I bypassed the block vent switch and the burners came on so it’s definitely the block vent switch tomorrow a licensed plumber is coming to change it and no worries boiler is off we have all over the home fire/carbon monoxide alarms and pilot is off thanks for your help
 
  #5  
Old 10-20-19, 06:02 PM
poorplmbr's Avatar
Member
Join Date: Feb 2003
Location: long island ,new york
Posts: 317
Received 16 Upvotes on 15 Posts
Plumber coming

Make sure the plumber checks your flue and chimney! There is usually a reason the blocked vent switch trips!
 
  #6  
Old 10-20-19, 07:06 PM
L
Member
Thread Starter
Join Date: Oct 2019
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Is that for gas burners ? Check chimney and flue does that need cleaning ?
 
 