Boiler Buderus G115ws
#1
Member
Thread Starter
Join Date: Dec 2008
Location: Washington PA
Posts: 241
Received 0 Votes
on
0 Posts
Boiler Buderus G115ws
I am looking at the manuel that says to put the baffles in the horizontal position. There is a diagram that shows the ends of the baffles, but I don't know which way is horizontal. The baffles are triangular.
Anyone know ?
Thanks
Anyone know ?
Thanks
#3
I was looking at the same diagram.
It looks like they are illustrating the final position that the baffles should be in.
It looks like they are illustrating the final position that the baffles should be in.
#5
Member
Thread Starter
Join Date: Dec 2008
Location: Washington PA
Posts: 241
Received 0 Votes
on
0 Posts
So the service guy came to set my boiler too specs. The stack temperature he measured was 260°. The book says spec is 326°. He seemed unconcerned with the lower temperature. I suggested adjusting baffles as per the book, but he thought uneccesary. Saying it was above the temperature that condensation would occur,,and it might "screw something else up".
He was new to both Buderus oil boiler and Riello burners. He is the oil burner guy for the company he works for.
Should I pull a pair of baffles to increase stack temp by 40°, as per the book, or is this not recommended?
He was new to both Buderus oil boiler and Riello burners. He is the oil burner guy for the company he works for.
Should I pull a pair of baffles to increase stack temp by 40°, as per the book, or is this not recommended?
#6
84,
From personal experiences my suggestion, especially with Riello would be to follow their recommendations and get someone who is familiar with working on Riello's. They are not like Beckett or Carlin burners. They must be set up to their specs. At the very least if you are unsure I would call Rielolo and see what they recommend.
This is just my opinion but when I was doing service I can't tell you the number of problems I solved just by setting up the burners the proper way after a tech had just did what he would do on a normal burner which went from wrong nozzle to the wrong pump pressure and baffeling.
In my area and I'm sure others they recommeneded and held classes to work on these burners. It wasn't mandatory but it was highly recommended with a certificate given on completion in case of problems.
Hope this helps a little.
From personal experiences my suggestion, especially with Riello would be to follow their recommendations and get someone who is familiar with working on Riello's. They are not like Beckett or Carlin burners. They must be set up to their specs. At the very least if you are unsure I would call Rielolo and see what they recommend.
This is just my opinion but when I was doing service I can't tell you the number of problems I solved just by setting up the burners the proper way after a tech had just did what he would do on a normal burner which went from wrong nozzle to the wrong pump pressure and baffeling.
In my area and I'm sure others they recommeneded and held classes to work on these burners. It wasn't mandatory but it was highly recommended with a certificate given on completion in case of problems.
Hope this helps a little.
#7
Member
Thread Starter
Join Date: Dec 2008
Location: Washington PA
Posts: 241
Received 0 Votes
on
0 Posts
Spott, thanks for the feed back !
I live near Pittsburgh, have not found anyone that knows Reillo yet. They are uncommon in this area. The other specs including pump pressure were set to the book numbers.
So I ran an experiment after the tech left.
The hydrostat is a Fuel Smart 3250plus and on a new heat call, it will fire and heat water up to 150° then shutoff before thermostat satisfied, a few minutes later, refire and heat up to 165° shutoff, and keep repeating this cycle, each time water temp climbing higher toward max temperature until thermostat satisfied.
I watched the stack temperature during this whole cycle process and it too would rise to an increasingly higher temp. during each cycle, (stack temperature falling back when flame
out) maxing out at 290°. (30° higher than the 260° the tech measured). This is part of the Fuel Smart efficiency scheme, not heating to max water temperature initially, until the unit samples how often heat calls are made in response to flame on heat cycles.
My point is two things, first, given more time than the tech gave it, the stack temperature rose to 290°
which is a lot closer to the spec of 326° than the 260° he measured. Second, this hydrostat seems as if it is designed to maintain water temperature and stack temperature below max values a lot of the time for fuel efficiency. This puts me back to wondering about low stack temperature condensation. Any thoughts ?
I live near Pittsburgh, have not found anyone that knows Reillo yet. They are uncommon in this area. The other specs including pump pressure were set to the book numbers.
So I ran an experiment after the tech left.
The hydrostat is a Fuel Smart 3250plus and on a new heat call, it will fire and heat water up to 150° then shutoff before thermostat satisfied, a few minutes later, refire and heat up to 165° shutoff, and keep repeating this cycle, each time water temp climbing higher toward max temperature until thermostat satisfied.
I watched the stack temperature during this whole cycle process and it too would rise to an increasingly higher temp. during each cycle, (stack temperature falling back when flame
out) maxing out at 290°. (30° higher than the 260° the tech measured). This is part of the Fuel Smart efficiency scheme, not heating to max water temperature initially, until the unit samples how often heat calls are made in response to flame on heat cycles.
My point is two things, first, given more time than the tech gave it, the stack temperature rose to 290°
which is a lot closer to the spec of 326° than the 260° he measured. Second, this hydrostat seems as if it is designed to maintain water temperature and stack temperature below max values a lot of the time for fuel efficiency. This puts me back to wondering about low stack temperature condensation. Any thoughts ?
#8
84,
Listed below is a sight where you can scroll to install instructions and it will tell you everything you need to know about your control depending what you have for a system, meaning zones and hot water. Condensation happens around 125 which your control prevents I believe.
https://www.supplyhouse.com/Hydrolev...hoClt0QAvD_BwE
Hope this helps a little.
Listed below is a sight where you can scroll to install instructions and it will tell you everything you need to know about your control depending what you have for a system, meaning zones and hot water. Condensation happens around 125 which your control prevents I believe.
https://www.supplyhouse.com/Hydrolev...hoClt0QAvD_BwE
Hope this helps a little.
#9
Condensation is a 133 F and leads to sulfuric acid and boiler deterioration, so should be avoided.
84EdH stack temperature is way higher than 133 F.
Stack temperatures below 300 F reflect high efficiency, 85% or more.
Consider manufacturer's spec to be limits, not goals.
84EdH stack temperature is way higher than 133 F.
Stack temperatures below 300 F reflect high efficiency, 85% or more.
Consider manufacturer's spec to be limits, not goals.
Last edited by doughess; 11-08-20 at 09:18 AM.
#10
Member
Thread Starter
Join Date: Dec 2008
Location: Washington PA
Posts: 241
Received 0 Votes
on
0 Posts
It makes sense to see the spec of 326 as a limit, not a goal. However. The manuel goes through some detail showing how to raise stack temp by adjusting or removing baffles.
#11
Adjusting baffles is about optimizing boiler heat transfer efficiency.
Combustion efficiency is a different issue.
Both use stack temperatures for reference.
Heating cost rise with higher stack temperatures.
Combustion efficiency is a different issue.
Both use stack temperatures for reference.
Heating cost rise with higher stack temperatures.
Last edited by doughess; 11-10-20 at 09:23 AM.
#12
Member
Thread Starter
Join Date: Dec 2008
Location: Washington PA
Posts: 241
Received 0 Votes
on
0 Posts
So, as long as I am not getting condensation in the chimney, lower temps are better (assuming combustion side of things is happy).
Where and how do I check for effects of condensation if I had it ?
Where and how do I check for effects of condensation if I had it ?