Installing wifi thermostat to boiler system
#1
Member
Thread Starter
Join Date: Nov 2020
Posts: 1
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Installing wifi thermostat to boiler system
Have a pretty basic Honeywell digital thermostat hooked up to my cottages gas
boiler system ( No AC) and would like to replace it with the Honeywell RTH6580WF smart thermostat. The existing wiring it connected to R and W no extra wires in the wall and the thermostat is battery powered, is a C wire needed and do I need any other connections from the furnace.
boiler system ( No AC) and would like to replace it with the Honeywell RTH6580WF smart thermostat. The existing wiring it connected to R and W no extra wires in the wall and the thermostat is battery powered, is a C wire needed and do I need any other connections from the furnace.
#2
Member
Yes, a C wire is required. See manual: https://www.honeywellstore.com/store...thermostat.pdf Here is another option that doesn't require a C wire, but it is not WiFi enabled: Honeywell TH6100AF2004
#3
Hi, yes you will need a 3rd conductor, it maybe best to pull a new 18/3 thermostat cable from the boiler to the Stat, post some pics of your boiler controls and we can assist with the connections, good choice for the Stat.
Geo🇺🇸
Geo🇺🇸
#4
Member
Electronic thermostats are powered with 24 volts AC on terminals C and RH.
There is a an alternative to installing new 3 wire cable.
Near thermostat install a 120 volt - 24 volt adapter and connect to C and RH. Existing two wires still go to RH and W.
It is an easy way to upgrade older home that have thermostats on 2nd and 3rd floors.
https://www.amazon.com/s?k=120+volt+...ref=nb_sb_noss
No other connections are need from boiler unless there is a fan on system.
There is a an alternative to installing new 3 wire cable.
Near thermostat install a 120 volt - 24 volt adapter and connect to C and RH. Existing two wires still go to RH and W.
It is an easy way to upgrade older home that have thermostats on 2nd and 3rd floors.
https://www.amazon.com/s?k=120+volt+...ref=nb_sb_noss
No other connections are need from boiler unless there is a fan on system.