I'm posting this information as a data point for whatever use the readers wishes to make of it.
This for a 70-year-old Kewanee hot-water boiler. Fire-tube, two pass, natural gas, 168,000 Btu net rating.
Stack temperature - 442 deg F gross, 366 deg net.
8% CO2
20% stack loss
80% boiler efficiency
This boiler is installed on a 3,900 sq ft, two-story, frame house with new windows and average insulation (for 1951)
Calculated heat loss using Slant/Fin Hydronic Explorer, before window replacement: 106,000 Btu/hr (27.2 Btu/ sq ft). Indoor design temp 70 deg F, outdoor design temp -10 deg, design water temp 180 deg.
This for a 70-year-old Kewanee hot-water boiler. Fire-tube, two pass, natural gas, 168,000 Btu net rating.
Stack temperature - 442 deg F gross, 366 deg net.
8% CO2
20% stack loss
80% boiler efficiency
This boiler is installed on a 3,900 sq ft, two-story, frame house with new windows and average insulation (for 1951)
Calculated heat loss using Slant/Fin Hydronic Explorer, before window replacement: 106,000 Btu/hr (27.2 Btu/ sq ft). Indoor design temp 70 deg F, outdoor design temp -10 deg, design water temp 180 deg.