Annual maintenance for Utica water heater system


  #1  
Old 11-26-20, 12:26 AM
R
Member
Thread Starter
Join Date: Nov 2020
Posts: 10
Received 0 Upvotes on 0 Posts
Smile Annual maintenance for Utica water heater system

Hello folks,

I have this Utica radiant heating system and has worked great with annual maintenance. Last two years, the local AC and heat co. sent this much inexperienced tech and he is done in 10 minutes whereas the much seasoned tech took about 40 minutes to perform the annual service in prior years - there's other mistakes he made and then wanted to

Utica Boiler model MGB75HID
charge me to drive back and undo his mistake - also turned the water intake off and when I called to ask why the pressure has been stuck at zero, he said the gauge is bad.

Anyway, I think I can do the maintenance myself if I had a guide to follow or a video. Last two days, the heat is off in the morning and I need to power cycle it a few times to get it going again - possibly the flame sensor or thermopile.

If anyone could point me in the right direction, it would be much appreciated.
 
  #2  
Old 11-26-20, 09:21 AM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Here is the manual for your boiler: https://uticaboilers.com/sites/default/files/2426.pdf
 
radioguy80 voted this post useful.
  #3  
Old 11-27-20, 12:27 AM
R
Member
Thread Starter
Join Date: Nov 2020
Posts: 10
Received 0 Upvotes on 0 Posts
Thanks, Grady

Looking at Pages 20 and 25, I see there is a thermocouple and the 1/4" pipe in my system runs gas to the pilot. I guess I have to get in there and start pulling things apart.
 
  #4  
Old 11-27-20, 01:19 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,512
Received 3,485 Upvotes on 3,128 Posts
You should know whether your boiler has a standing pilot which uses a thermocouple or a boiler that has electronic ignition if you're going to be servicing it.

Yours doesn't have a thermocouple..... it's electronic ignition.
The manual covers both types. You have a white ignition module on your boiler.
You should be hearing the ignition spark when the pilot lights before the burner lights.

1) Do you see the draft damper opening on a call for heat ? Is it opening all the way ?
2) Do you hear the spark ignition ?
3) If you don't hear the spark ignition...... check for 24vAC on terminals 5 and 6 on the spark module. That would be the same as checking terminals B1 and B2 in the aquastat. If there is no 24v then you need to check for 24v passing thru the damper and returning back to the aquastat.

Those draft dampers are a common problem area.
I see a piece of pipe with a cap on it on top of the boiler..... I hope that's not being used in the pressure relief valve line.
 
radioguy80 voted this post useful.
  #5  
Old 11-27-20, 03:03 AM
R
Member
Thread Starter
Join Date: Nov 2020
Posts: 10
Received 0 Upvotes on 0 Posts
Thanks for the detailed reply, Pete.

When the thermostat sends the signal, I can hear the 2 second squeal which I assume is the draft damper

Then I hear the spark ignition and after about 5 seconds the burners come on

But even today, the temps fell to 65f inside (its set to maintain 71f ) and the heat symbol was blinking in the thermostat but the unit came on after I power cycled it. Seems to me like it needs a power cycle once a day as it just came on by itself while I was typing this reply.
 
  #6  
Old 11-27-20, 08:14 AM
Grady's Avatar
Forum Topic Moderator
Join Date: Jan 2005
Location: Delaware, The First State
Posts: 12,667
Received 39 Upvotes on 37 Posts
Intermittent problems are the toughest to troubleshoot. What you describe is often caused by a sticking draft damper BUT not always.
 
radioguy80 voted this post useful.
  #7  
Old 11-28-20, 08:45 AM
poorplmbr's Avatar
Member
Join Date: Feb 2003
Location: long island ,new york
Posts: 307
Received 15 Upvotes on 14 Posts
If the boiler is igniting and then going out, you probably need to clean or replace your spark ignition pilot assembly. Seems like it is not recognizing flame.
 
radioguy80 voted this post useful.
  #8  
Old 11-29-20, 03:24 PM
R
Member
Thread Starter
Join Date: Nov 2020
Posts: 10
Received 0 Upvotes on 0 Posts
I see a piece of pipe with a cap on it on top of the boiler..... I hope that's not being used in the pressure relief valve line.
That has been there since I moved into this house 5 years ago.
 
  #9  
Old 12-17-20, 02:32 PM
R
Member
Thread Starter
Join Date: Nov 2020
Posts: 10
Received 0 Upvotes on 0 Posts
Smile Wiring help needed for pilot control module

So the parts came in and I am ready to replace the intermittent pilot control module.


How do I Prepurge and Trial for Ignition timing dipswitches


Do I wire in exactly as the old one or should I not connect the 24V. I ask because the manufacturer sent an email with this ...


IMPORTANT
  • "TH-W" terminal should be connected to the "W" terminal from the thermostat
  • "24V GND" terminal should be connected to the unswitched leg of the 24VAC transformer
  • "24V" terminal should NOT be connected unless you have a functioning vent damper connected to the "P1" vent damper plug. Note that once the module works with a vent damper for 10 ignition sequences, it will no longer work without a functional vent damper after that.
  • Read the instructions to set Prepurge and Trial for Ignition timing dipswitches before applying power. Once the module starts the 20th “Call for Heat”, the control operating sequence is permanently locked and cannot be reset by resetting the Dip Switches.


Thanks!



Old Pilot controller

Pilot and Thermocouple

Replacement I ordered - looks too big

Replacement I ordered - need wiring advice
 
  #10  
Old 12-17-20, 03:12 PM
S
Member
Join Date: Oct 2013
Location: United States
Posts: 2,724
Received 132 Upvotes on 124 Posts
What you bought was a thermocouple, what you needed was a pilot assembly. Below is a sight where you will find examples of what you should have bought. If you call them and give them the model number of your boiler unless you have the parts list with the number they may be able to help you.

https://www.supplyhouse.com/sh/contr...pilot+assembly
 
radioguy80 voted this post useful.
  #11  
Old 12-17-20, 03:58 PM
R
Member
Thread Starter
Join Date: Nov 2020
Posts: 10
Received 0 Upvotes on 0 Posts
Thanks, spott - I looked it up and called them; to me it looks like this one

https://www.supplyhouse.com/Utica-Du...Pilot-Assembly

After providing the model, etc for my Utica, they think it is this one

https://www.supplyhouse.com/Utica-Du...Pilot-Assembly

I don't see this one in there. They recommended I call Utica and provided the ph nr.
--------------------------------------------------------------------------------------------------------------
Reading around for the connections, it appears I should use the TH-W terminal for 24v and leave the 24v terminal unused.

 
  #12  
Old 12-17-20, 04:24 PM
S
Member
Join Date: Oct 2013
Location: United States
Posts: 2,724
Received 132 Upvotes on 124 Posts
As far as your control goes there are different brands out there and it depends what you currently have. I personally have not put one in in a while but when I did it on a regular basis I did have to make some wiring changes to the new ones depending what brand. If I were you to save some headaches I would call google Honeywells number unless it's in the instructions and ask for technical. Have your old control number and boiler numbers and they will be happy to help you.

Another way to do it is to go to the Honeywell sight and in a section they will have a cross reference section and describe what goes where.

What is your current brand and model and your new Honeywell model. They will all work but they just want the wires in a different place sometimes.

Go to the install instructions and scroll down to about page 8 or read the whole thing. It may help.

https://www.supplyhouse.com/Honeywell-S8610U3009-Intermittent-Pilot-Control-4584000-p?gclid=CjwKCAiAoOz-BRBdEiwAyuvA63AIWQyUhgp6Dxek2vdY7_h-BTi96v4yY0EjUupckIu04Q2cw3dOjBoC_oIQAvD_BwE
 
radioguy80 voted this post useful.
  #13  
Old 12-17-20, 04:39 PM
R
Member
Thread Starter
Join Date: Nov 2020
Posts: 10
Received 0 Upvotes on 0 Posts

Honeywell S8610U3009

I think I'm good with the wiring, There is no vent damper connected to my existing spark control module, it's wired to the aquastat therefore I'll only connect the old 24v cable to the th-w terminal

Do I need to worry about the dip switches for the Trial for Ignition (TFI) as shown here

https://literature.neuco.com/S8610Utshoot.pdf
 
  #14  
Old 12-17-20, 05:36 PM
R
Member
Thread Starter
Join Date: Nov 2020
Posts: 10
Received 0 Upvotes on 0 Posts
Nope, I wasn't

Attaching the 24v hot to the TH-W did not nothing; it doesn't come one or any indication its doing something.

I have the old one hooked up again because it started getting a little cold for my young ones.
 
  #15  
Old 12-19-20, 07:13 PM
R
Member
Thread Starter
Join Date: Nov 2020
Posts: 10
Received 0 Upvotes on 0 Posts
Thanks for the reply and the link;

I have installed it as per page 8, I have the 8600M. I used the TH-W and it kicked off the furnace once and since then it gets the heat signal, the squealing noise happens (damper opening I'm guessing) and no spark noise.

I also received and installed the pilot assembly unit a few hours ago

https://www.supplyhouse.com/Utica-Du...Pilot-Assembly

I installed both parts at the same time and it has worked only once since, a few hours ago.
 
  #16  
Old 12-19-20, 07:45 PM
R
Member
Thread Starter
Join Date: Nov 2020
Posts: 10
Received 0 Upvotes on 0 Posts
This is the draft damper motor

 
 