I noticed today that my baseboard was not heating up even though the boiler is running and the zone is opened. I figured out that the circulating pump was not running. I have an Aquastat relay L8148A. I tested at C1 and C2 and no power. I tested the pump manually to an outlet and it runs fine. Here's the weird part. When the pump is disconnected at the relay I do get 118 volts at C1 and C2. But when I connect the pump back to the relay I get no power.
p,
Try jumping TT on your control and see if your clapper opens and if your pump comes on or if you get power to C1 & C2. If the pump works independently it could be a bad solder connection in the control. Those aquastats are known for that they start to work inconsistant unless you have loose wiring in the pump itself.
Spott,
I disconnected the board and took a picture of the back before I read you reply. It doesn't look like any bad solders. When you mean "clapper" I assume you mean the magnetic thing. That does activate when heat is called. Here's a picture of the back. I could not take the thermocouple out as it's stuck and don't want to break it.
Try jumper on B1 to C1 the circulator should start. If starts then relay 'clapper" in L8148A is bad.
With modern, high sensitivity meter 118 volts measured between C1 and C2 may indicate bad relay contacts . When circulator motor connected resistance of those contacts limits current and motor does not start.
Wire 120 volt pilot light to circulator motor to see powerd on. Makes systen diagnostics easier.
Honeywell L8148A is old technology product. For same price replace it with Tekmar out-door-reset/ aquastat than may save up 20% on fuel costs. Also is more reliable, accurate with numerous benefits and features. Just remove L8148A sensor and use L8148A for 24 Volts to power Tekmar.
I put a test light on the circulator motor and jumped B1 to C1 and the motor came on. I guess I need a new L8148A. Can I leave it jumped until I get a new board? I've been powering the circulator motor from an outlet and left it always running with one zone constantly opened.
p,
No problem B1 - C1. When burner comes on pump will come on. The thing is that if the burner shuts off on limit so will the pump and the stat might not be satisfied.
Do you only have 1 zone. My guess is no tankless because that is only a high limit aquastat. If you have more than 1 zone you can manually open your flocheck valve and whenever any other zone calls it will heat that zone also. The drawback to that is it might get a little warm from the other zones calling for heat.
p,
No problem B1 - C1. When burner comes on pump will come on. The thing is that if the burner shuts off on limit so will the pump and the stat might not be satisfied.
Do you only have 1 zone. My guess is no tankless because that is only a high limit aquastat. If you have more than 1 zone you can manually open your flocheck valve and whenever any other zone calls it will heat that zone also. The drawback to that is it might get a little warm from the other zones calling for heat.
I have five zones, 4 for baseboard heat and 1 for an indirect water heater. I will jump B1 -C1 for now until I get a new Aquastat. Is there a better relay I can buy to replace this one? The system was built in 1995 and the first crapped out about 5 years ago. Not bad for twenty years, but 5 years on the second?
For same price replace L8184A with Tekmar 256 and save up to 20% on fuel costs. A side benefit of ODR/A's is more comfortible home. Heating element water temperatue varies according to outside temperature.
A Honeywell out door reset aquastat setup costs $450+
Honeywell for the past 30 years has been milking the old products and not investintg in new technoloy.
Honeywell no longer makes thermostats, just licenses name to other companywhose units have many issues. DH just returned two of their new programable Wi-Fi thermostats.
Now I'm really confused. Please excuse the ignorance as I'm a newbie to all this. I searched the Tekmar but i am not sure how would I install this in place of the L8148A.
I’m no expert but I think the Tekmar does not replace the 8148. The Tekmar measures outdoor temps along with boiler water temp (I think you strap a water temp sensor somewhere on your pipes, pretty sure), and it also gets input from the thermostat (heat call), and from all that decides when/if to turn on the boiler. (I think that it would send the T-T signal to your 8148 when it wants the boiler to come on).
I don’t think the Tekmar would have any kind of safety limit like the High Limit provided by the 8148.
I don’t see how it’s a replacement for the 8148, but maybe it is. I guess “D” and the other boiler guys here will clarify things.
p,
You are not confused or wrong. As Z pointed out it does not take the place of your aquastat. This has been an age old discussion that I have just given up on with the poster. We just have different opinions on the subject. The purpose of the Tekmar is to ajust the water temp according to the outdoor temp for possible fuel savings and not to be used as a high limit. You still need your aquastat but I'm sure there will be disagreements.
Do your research before diving into one of these Tekmars.
Tekmar 256 is used for high safety limit. It is aquastat with both low and high limit settings, in 1 degree increments. High and low have separate delt-T options.
Thermostats sensing room heat on hydronic systems issue "call for heat" to start circulator. Aqustats sensing boiler water temperature issue "call for heat" to start boiler/burner.
The original aqustats were only a two terminal temperature activated switch wired to start burner. Different meaings of "aqustat" causes frequent issues on DIY.com
Tekmar also has out-door-reset to lower fuel costs make for more comfortible home. Put simply modern aquastat with ODR have major benefits over old. Price of old and new is similar but cost savings are major, tangible benefit.not available on old technology Honeywells.
When DH has to replace defective part, look for something that will also improve system performance, reliability and reduce costs.
Hi,
I have just installed a new Drayton zone replacement valve , model ZA5.
The good news is that the value is working; however, the issue I'm experiencing is that when my thermostat turns the central heating on, the valve moves to the off position and the valve closes and when I turn off the central heating from the thermostat the valve moves to the on position and the valve opens.
I have a hive thermostat already installed.
Any idea what's happened and how I can fix this?
I've tried my best to place the wires in the exact same place where I removed the old value wires but as you will see the wiring/control centre is a shambles.
Please let me know if you require more pictures or information.
Thank you
Meethi
[img]https://cimg0.ibsrv.net/gimg/www.doityourselft.com-vbulletin/2000x1504/20210220_142720_61324635ffd5072c6ff3276c9619136c0788bc6a.jpg[/img]
Have a Burnum 3 zone boiler. Woke up with no heat in one zone. Taco 007 f5 Circulating pump was replaced and bled the system. Circulating pump is humming however the pipes above it are not getting hot. When I turn up the heat we hear the clicking sound but no heat. Other 2 zones work as expected.