Taco SR502 no lights please help


  #1  
Old 01-28-23, 06:15 AM
E
Member
Thread Starter
Join Date: Jan 2023
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thumbs down Taco SR502 no lights please help

Taco SR502 installed nest all was good 2 days. now no power to RH message on nest , no power to common on all the other thermostats. and no power to common and 24v on sr502 board.
The Taco sr502 has no lights on at all .
fuse is good what can I do next?

 

Last edited by PJmax; 01-29-23 at 01:40 PM. Reason: reoriented/enlarged pic
  #2  
Old 01-28-23, 07:58 AM
B
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 2,664
Received 235 Upvotes on 208 Posts
Green LED off indicates no 120 vac. Measure voltage at SR502 or check the breaker
 
  #3  
Old 01-28-23, 08:43 PM
D
Member
Join Date: Apr 2014
Location: us
Posts: 1,300
Received 100 Upvotes on 94 Posts
Heating systems status diagnostics the easy cheap way

On heating systems pilot lights (120 or 24 volt) on zone valves, pumps, aquastat, transformers, etc..
make it easy to see status and quickly trouble shoot problems, especially on multi zone systems,

When wife says no heat in some room. Can see whether that thermostat is calling for heat, zone valve open, circulator running, boiler aquastat calling for heat, burner on, etc. etc. Sometimes reason for no heat was someone forgot to turn up thermostat. Duh, Duh.

Lights are cheap, $20 goes a long way
https://www.amazon.com/dp/B0B28JBY7M/ref=sspa_dk_detail_6?pd_rd_i=B0B28JBY7M&pd_rd_w=7yrRW&content-id=amzn1.sym.98eae024-ddf8-4aae-a3d1-746298cd5013&pf_rd_p=98eae024-ddf8-4aae-a3d1-746298cd5013&pf_rd_r=NGCWFBQS04098HAXZ75S&pd_rd_wg=kXVnP&pd_rd_r=9a442b78-fd69-4dd8-8107-18f0abc4d4d0&s=automotive&sp_csd=d2lkZ2V0TmFtZT1zcF9kZXRhaWxfdGhlbWF0aWM&spLa=ZW5jcnlwdGVkUXVhbGlmaWVyPUFEMEhQVzBNMzUwR00mZW5jcnlwdGVkSWQ9QTAyODcwMzEzSTdVV0JQWks4MTBOJmVuY3J5cHRlZEFkSWQ9QTA4OTU2OTNDRVVVWjQxMTdSNkwmd2lkZ2V0TmFtZT1zcF9kZXRhaWxfdGhlbWF0aWMmYWN0aW9uPWNsaWNrUmVkaXJlY3QmZG9Ob3RMb2dDbGljaz10cnVl&th
 
  #4  
Old 01-29-23, 11:11 AM
B
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 2,664
Received 235 Upvotes on 208 Posts
OP said none of the status lights in the SR502 are on so some status indication is provided. Green light ON means SR502 has 120 vac. I would be leery of the lights suggested in post 3. They are not UL approved and have a metal body. If the hot 120/240 vac wire makes contact with the metal body, the metal body and anything it touches becomes a shock source unless grounded or a protection device opens circuit.
 
  #5  
Old 01-29-23, 12:30 PM
D
Member
Join Date: Apr 2014
Location: us
Posts: 1,300
Received 100 Upvotes on 94 Posts
Link in DH Post #3 showed many types of pilot lights, But not how to use them.

Comment in Post #4 about UL not approved does not apply to home owner system changes.

UL is used by manufactures of products. “Underwriters Laboratories UL Solutions delivers testing, inspection and certification services, together with software products and advisory offerings, that support our customers' product innovation and business growth.


National Electrical Code (NEC) is for building wiring, electrical service, not things connected to it

​​​​​​​NFPA 70, is the benchmark for safe electrical design, installation, and inspection to protect people and property from electrical hazards.
 
  #6  
Old 01-29-23, 01:55 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
WAY TOO MUCH static here.

The SR-502 has LED's on it Doug,
There is no need for additional LED's if the factory ones are not working.

EV..... welcome to the forums.

I see your SR-502. I see 2) two wire thermostat cables.
I see some kind of splice at the C/24v terminals.
How can your nests possibly be showing a common problem with no C connection ?
With two wires on the SR-502 you should be connecting to R and W on the thermostats.
That would mean no C connection and a good chance the nests will not work there.

If you have 120vac present to the unit and the fuse is good..... the transformer is blown.
It's only a 15va transformer..... not much room for connection or load errors.
 
  #7  
Old 01-29-23, 07:02 PM
D
Member
Join Date: Apr 2014
Location: us
Posts: 1,300
Received 100 Upvotes on 94 Posts
Readers might note words in Opening Post#1 "The Taco sr502 has no lights on at all."

DH comment: SR502 LED’s do not have power ON light. Only LEDs that light to show which zone active.

Taco would raise costs and lower profits putting On LED light on R502. But DIY’s can add their own.

Solving DIY issues is often made more difficult s by "static" words in posts who do not read, or understand issues.
See Post.#6 "WAY TOO MUCH static here. The SR-502 has LED's on it Doug, There is no need for additional LED's if the factory ones are not working."
 

Last edited by doughess; 01-29-23 at 07:25 PM.
  #8  
Old 01-30-23, 05:54 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
Yes Doug... member said no lights on at all.
That would be correct if the unit is dead as it does have a green power LED.

Most of the Taco controllers have a power LED.
 
  #9  
Old 01-30-23, 09:12 PM
D
Member
Join Date: Apr 2014
Location: us
Posts: 1,300
Received 100 Upvotes on 94 Posts
SR502 controls do not have lights showing 120 V power to circulators N H terminals.

Green LED shows power on to SR502, red LEDs show which circulator circuit has been activated.(and hopefully powered if fuse has not blown.

DH puts 120 volt light on Burner System on off Switch and SR502 output terminals N H and on circulator motors.
 
  #10  
Old 01-31-23, 05:15 PM
rbeck's Avatar
Member
Join Date: Jul 2007
Location: United States
Posts: 2,394
Upvotes: 0
Received 61 Upvotes on 51 Posts
Getting back to business.
Do you have 120V at INPUT 120V terminals?
If yes, pull the fuses and check for continuity on fuses.
The green light looks like it could be in trouble and why it may not be lit.

 
  #11  
Old 01-31-23, 06:05 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
The OP has stated fuse is good and no power on R and C.
You can't see the R and C terminal strip as it's in the upper left corner of the board.

More than likely the OP didn't realize there is a polarity on the TT terminals when a C is involved.

We need to hear back from the OP now.
 
 