12 or 14 gauge extension cord?

I am in the process of purchasing a Firman 4550/3650 remote start gas generator, and have read online that 12 gauge extension cords are for 20 amp circuits while 14 gauge are for 15 amp circuits. The specs for my machine says the 120 V. AC outlets are 20 amp. I plan to run a 600 watt manual/rotary microwave oven, and also a 1500/750 Watt space heater this winter. Should I buy a 12 gauge extension cord?

For electronic devices such as laptop, phone, tablet, headphones and such, should I buy just a regular 16 gauge extension cord?
 
  #2  
Old 09-27-19, 03:17 PM
T
Member
Join Date: Jan 2015
Location: USA
Posts: 844
Received 87 Upvotes on 77 Posts
Your numbers are basically correct although the 12 gauge would be a twistlock. However, depending on the length of your cord, voltage drop could require a thicker gauge.
 
  #3  
Old 09-27-19, 04:54 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,057
Received 3,420 Upvotes on 3,066 Posts
The 4550/3650 is peak and running wattage. Not the model number.
They have several models listed with these rating. Which model are you looking at ?
 
  #4  
Old 09-28-19, 02:35 AM
M
Forum Topic Moderator
Join Date: Mar 2005
Location: USA - N.E.Tn
Posts: 45,162
Received 741 Upvotes on 647 Posts
How long the extension cord needs to be can also be a determining factor as to what gauge you need.
 
  #5  
Old 09-28-19, 05:44 AM
F
Member
Thread Starter
Join Date: Jul 2015
Location: United States
Posts: 74
Upvotes: 0
Received 0 Upvotes on 0 Posts
I will be using 75 to 100 feet of extension cord.
 
  #6  
Old 09-29-19, 03:00 AM
M
Forum Topic Moderator
Join Date: Mar 2005
Location: USA - N.E.Tn
Posts: 45,162
Received 741 Upvotes on 647 Posts
While I'm familiar with using a generator for painting and construction tools, I don't really know anything about your proposed use BUT I would go with a 12 gauge cord for that distance to combat any voltage drop.
 
  #7  
Old 09-29-19, 11:34 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,057
Received 3,420 Upvotes on 3,066 Posts
Since you didn't post the model number..... we'll assume you have one duplex receptacle. That means that each half of that receptacle is one circuit. You need to run an extension cord from both halves of the receptacle. You should be using a #12 extension cord for the heater regardless of the length and it should be the only device on that cord. You could use #12 or #14 for the second cord to run everything else.
 
  #8  
Old 09-29-19, 02:56 PM
F
Member
Thread Starter
Join Date: Jul 2015
Location: United States
Posts: 74
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the input.

When you say the second cord could be #12 or #14, does that mean for low impact electronic devices like phones, tablets, laptops, headphones and such, in which case I would plug in a usb hub with about 4 ports to charge as many small devices as possible at the same time. 16 gauge at 75 or 100 feet would not work?
 
  #9  
Old 09-29-19, 06:12 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,057
Received 3,420 Upvotes on 3,066 Posts
#16 wire at 100' is relatively small. You'd need to limit the wattage to well under 1000w.
 
  #10  
Old 09-29-19, 07:47 PM
F
Member
Thread Starter
Join Date: Jul 2015
Location: United States
Posts: 74
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes, that's what I'm saying; these devices I mentioned are well under a 1000 watts. I just thought there might be a problem with the amount of length needed for the extension cord. So, I will get a 16 gauge for my small electronic devices, and 12 gauge for the space heater and microwave which I will not run at the same time.

Hope that will do it.

Thanks a lot for the help.
 
 