APC Back-UPS Office 500 VA


  #1  
Old 05-13-08, 08:55 AM
B
Member
Thread Starter
Join Date: Jun 2002
Location: Northern Minnesota
Posts: 1,628
Received 13 Upvotes on 9 Posts
Question APC Back-UPS Office 500 VA

Yesterday the power went out for maybe one second and came back on.

Instead of running off the UPS the computer and monitor shut off. Received a steady alarm and yellow light (battery running low) for about a minute then the red light (replace battery) came on and the UPS shut down.


Hmmm.....always worked correctly before, why not now? And seeing the power was only off for a second, why didn't it switch back to line power?

I bought the UPS in 01 so the battery is getting old but no low battery warning or anything like that.

Very confusing, any ideas?

Thanks,

Baldwin
 
  #2  
Old 05-13-08, 01:10 PM
Pendragon's Avatar
Member
Join Date: Jul 2002
Location: USA
Posts: 1,767
Upvotes: 0
Received 2 Upvotes on 2 Posts
You got 7 years out of that battery, so I'd say it did well.

If you are running the powerchute software, it ran a self test every week. If you aren't, then it never tested the battery under load.
 
  #3  
Old 05-13-08, 03:29 PM
B
Member
Thread Starter
Join Date: Jun 2002
Location: Northern Minnesota
Posts: 1,628
Received 13 Upvotes on 9 Posts
Thumbs up

"If you aren't, then it never tested the battery under load."

OHHH....I didn't know that. No, I didn't run the software because I always turned the computer off when I left and didn't think I needed it. Learn something every day.


I see a new battery is around $54 or I can trade this UPS in for a new one, 550 VA, for $56 with two more outlets. I think I'll go that route.

And I will run the software this time.

Thank you!


Baldwin
 
 